Gas supply line big - small - big
seldoon
Member Posts: 2
in Gas Heating
I'd like to replace a failed DV hot water heater with on-demand hot water heater. The gas supply line in question goes from the meter (AC-250) 1' @ 1" to 3/4 (1x3/4 Tee then a 3/4x1 coupling) to 1" (10') to 3/4 (62'). I could repipe 31' of the 3/4 to 1" without opening walls, but I can't find a resource to help me understand if I get any benefit from doing this. I would probably also fix the small mess at the meter end as well. My understanding of the longest run method is that repiping 31' from 3/4 to 1" doesn't buy me any benefit. Do I have this right?
Thanks for the feedback. The planned tankless is a 180k takagi, rated 5/10.5WC. I'm in Seattle, with PSE. The meter is an AC 250, " 250 CFH @ 1/2" Diff". Research suggests i have 7" WC at the meter. My appliances are rated to 5" WC, so i think I have 2" WC to work with.
A drawing of the run:
The current run is 1" rigid for A, then 3/4" CSST for B, C, D, E and G. F is 3/4" rigid. Also, B, C, D are actually a single piece, fwiw. The crux is that leg C runs inside a wall that I'd rather not open up.
If I can use leg C as is, and replace B, D and E with 1' CSST, I get a WC at the tankless of 5.337" with this option (C3). Calculations:
Per @mattmia2, it sounds like I can't do this option, but I'm unclear if that's what he's referring to above.
If using 1" pipe after 3/4" pipe is not allowed, then I would replace B with 1" CSST and C with 1" rigid (run outside for 14', then back inside). With this option (B) I get 5.10 WC at the tankless. Calculations:
Option B is a bit more work but still doable. There are other repiping combinations such as also changing D to 1" CSST (5.468" WC at the tankless) but these are the two I'm considering.
Any feedback appreciated.
You can also make up for some of your issues by using gas regulators.
However, if this was my house, I would not use a tankless water heater.0