G-1361 boiler
Levie
Member Posts: 89
I have this boiler and this is the only rating plate I can find on it very curious what the actual model number is and how many BTUs it is
I did see a model number online that was 61-13 that seemed quite similar and was wondering maybe they typed it in backwards? Or I might be way off0
The minimum relief valve capacity of 384 pounds per hour gives a clue as to the BTU rating. 970 BTU per pound of steam. 372,000 BTU.
Big house?—
Bburd0 -
Yes very big house probably about 4,200 square feet0
If this is natural gas fired, you can clock the test dials on the gas meter to see how much gas it's burning, then calculate the BTU input from there. Do this while all other gas appliances in the house are turned off.
One cubic foot of natural gas at standard temperature and pressure is 1,031 BTU. This may vary if you are in an area with an unusual gas supply. Your gas supplier can tell you.—
Bburd0 -
I did not think of that tnxbburd said:If this is natural gas fired, you can clock the test dials on the gas meter to see how much gas it's burning, then calculate the BTU input from there. Do this while all other gas appliances in the house are turned off.
One cubic foot of natural gas at standard temperature and pressure is 1,031 BTU. This may vary if you are in an area with an unusual gas supply. Your gas supplier can tell you.0
- 87.2K THE MAIN WALL
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 6.4K Radiant Heating
- 15.6K Strictly Steam