Get better at purging air?
watercourse
Member Posts: 33
Update, we're all purged! Just needed to run it in the opposite direction and off of an external water source instead of the plumbed in house water supply.
Any tips to purge air more effectively?
I have one loop (the one labeled family) that I've purged under house pressure four times and still every time I fire it up I get no flow. The last purge I let it run for over a half hour which seems like overkill. The water came out of the bleed hose fast and the bubbles stopped. Still no flow when the boiler is running, while all the other loops flow great.
I remember this loop gave me some trouble last time I drained and refilled too but don't recall how I finally got this loop moving.
I closed off my boiler and expansion tank, then cranked up the supply water valve pressure to the max it would allow which I think was 50psi. Then I opened each loop individually till the bubbles stopped.Then I leveled back the fill pressure and opened the boiler and expansion tank back up.Then I turned the system on and set it to send water through various loops to test. Got good flow everywhere except in this one loop.0
I hope that what ever zoning arrangement you have allows for the boilers minimum flow rate. One or two of those 1/2 loops is not enough. I see a lot of thermostat wires. 1 gpm per 10,000 btu. input is the standard. I seen it with less but..... it could be kettling to air lock.
- 119 Chimneys & Flues
- 76 Pipe Deterioration