Blue and Orange flame
josephny
josephny Member Posts: 428
I have a Burnham 204PVPI boiler with a VR8204C LP valve and fired it up for the first time.
The flames are mostly blue, but there is a substantial amount of orange.
Should I be concerned?
Is this something I can and/or should adjust?
Here is a video link:
https://youtube.com/shorts/mU-cK479mv4?feature=share
Thank you.
    HVACNUT Member Posts: 7,396
    First time ever?
    Was the boiler shipped for LP or was there a conversion kit?
    There's really nothing for you to do unless you're a heating tech. Lockup and manifold gas pressures need to be checked, as well as a combustion test.
    Mad Dog_2SuperTech
  • josephny
    Old boiler.  New to me house.
    I am (obviously) not a boiler tech. But I do work hard at learning to do stuff.
    Sounds like I need to check manifold pressure and do a combustion test.  Will research.
    Just using a little 20lb grill tank until lp company sets up large tank. I wonder if pressure is the culprit.
    Thanks.
  • Teemok
    Teemok Member, Email Confirmation Posts: 757
    The grill tanks can't vaporized liquid fuel to gas fast enough for most boilers. I would stop doing that. Wait until you have a proper fuel supply before checking the boilers tune condition further. Better safe than sorry with LP.
    bburd
  • josephny
    That's fascinating, and good to know.
    Thank you.