issue with converted gas power burner
zepfan
Member Posts: 444
in Gas Heating
We are having an issue with a Crown boiler that was originally oil fired. Model # CTPB-8 manufactured in 2003, converted to natural gas in 2017. That part was done by others. The unit has a Carlin ez pro gas burner control installed on it. The boiler has an identical model installed next to it that vents into the same chimney. That boiler which is the same model operates with no issues. The one with the issue comes on, proves flame, but then after about 10 seconds it sputters out, almost like it is back firing then loses flame. The heat exchanger is sealed and operates at a slight positive pressure about .01, where the stack pressure before the barometric damper is -.03. These readings, positive over the fire and negative in the stack is the same on both units. I removed the flue pipe check it, and the heat exchangers and both are clear and un obstructed. Also both the gas inlet pressure before the valve, and going to the burner are the same on both units. Any assistance/recommendations as to what could be causing this back firing/ sputtering out on the one unit would be greatly appreciated. Thanks to all
Run the burner with a pressure gauge connected to the downstream tap on the valve and your combustion analyzer set up and running. Does the gas pressure stay the same? Does the fuel-air mix stay the same?All Steamed Up, Inc.
Consulting2 -
Thanks for the responses Normally the boilers do not run in tandem. The controller stages them and the first stage is set for lead/ lag, so this problem is present with the sister boiler off. I connected a manometer to the inlet outlet ports on the gas valve, and the pressures seem constant the whole time this issue is occurring. 11” in 3.6” out unless the valave is sticking so fast that the meter can’t pick up the pressure fluctuation. Thanks again0
If there is way to post videos I can post a video of this condition, I did not see a way to do that0
To post a video, you need to post it on YouTube and post the link to that video. If you don't have a Youtube video account it is easy to make one. Just google the instructions. I used a FaceBook link to post a video on this site years ago, but that facebook account is long gone since my company was sold and I retired. (or I could tell you how to post a facebook video... But I need a millennial to do that for me since I'm a Boomer)
2 -
Thanks for all that responded to this. It turns out that making a slight adjustment to the air shutter from 70% to 80% made all the difference. The burner lite off smooth, and after running for a while, I did a combustion test ,and the readings and stack draft were good. The boiler is 256 mbh in, and while the instruction manual called for 70 %, it had to be set at 80% in order for the burner to stay online. Thanks to all0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 15.6K Strictly Steam