recirc with mixing valve
does anyone know if it makes a difference if the return line on a domestic system goes in to the cold supply anywhere or it needs to go close to the mixing valve ? , see attached drawing from a job we did and whenever it goes true the mixing valve the pumps are making problems and the mixing valve manufacture is saying we should add a bypass line see in red and its a lot of work to do just to try if it will solve the problem , does anyone have any input ? just to understand its a big building with 6 return pumps
maybe they think the domestic flow through the mixing valve plus the added pump flow is too much for the mixing valve so they want to inject the return water closer to the mixing valve. Does not seem like it would make a difference to me.0
It depends on the type of mixing valve. Does that brand shut off the cold port 100%?
There needs to be a path back to the tank to prevent recirc creep. The line will heat above mix valve setting if it creeps during periods of no or low use
https://www.caleffi.com/sites/default/files/file/idronics_11_na-r2.pdf
Two piping options for valves that close the cold port 10o%
What is the concern? Temperature droop or temperature creep? Unstable outlet temperature?Does that valve need a minimum flow to mix accurately? Most valves need a minimum gpm, so the piping and pump size needs to provide that If the building cannot.Bob "hot rod" Rohr
Living the hydronic dream0