Tekmar 364 problems
4035larry
Member Posts: 3
Hi All,
I just purchased a house in Gustavus, AK that has a boiler system with a Tekmar #364 controller. Now I am from the west coast and know almost nothing about a boiler system! Basically what is happening is the boiler is heating the water up to 170 degrees but the pumps are not coming on to distribute the hot water to the floor heating and hot water storage tank. We ran the "test" mode and all the pumps fired up and worked fine. We even had the original plumbing and electrical installer look at the unit with no results. Any insight or possible solutions would be GREATLY appreciated!
Thanks for the quick response guys! We had the wiring checked first thing against the schematic with the electrician who wired it and everything check out fine. I should have mentioned that when we first opened up the house the system worked (although sporadically) and failed to work at all after a power outage. Big Ed- This is a possibility on the temp sensor- where would I check that at?0
The outdoor sensor should be mounted on the North-West side of the building . It is a resistor you can check it with a ohm meter and the chart..
Download the manual. It tells you how to check everything with a meter.
If that checks out, then go thru the settings.
Then jump out to simulate a call for heat. The outdoor reset could be over ridden, or the sensor could be put in a cup of ice water if your above the WWSD temp.
You could also use a decade resistance box to simulate any outdoor temperature
You mentioned power outage. Maybe a spike caused some havoc.There was an error rendering this rich post.
If the pumps run in test mode and the display shows no errors, your issue lies in programming. The manual can be daunting and I agree the likely setting to address is “WWSD”, but if the system has activated this feature it will say so on the standby screen. Let’s use our available tools and post a picture or two of the unit’s display for a start.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
Hey guys- Thanks for all the suggestions! Turns out the number 3 pump was bad. Got it replaced and all is good now.0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 113 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
