The Holby Valve and multiple domestic HW temps
Mad Dog_2
Member Posts: 8,540
Someone had asked about doing this a few months ago, but I just dug out the picture from my archives. This was around 2013 in a NYC School. If I remember correctly the 3 temps were
120, 110, 105. It was a NYC School Construction Authority Sec. This spec is the last bastion of Old School Plumbing: All underground must be lead and oakum! I was in my glory. The SCA plumbing inspectors hold your measurements to 1/4"...YES! That fussy....Mad Dog
1
The Hobie mixing valve needs to be heat trapped
Check out the paper work from the manufacture .There was an error rendering this rich post.
I've seen the same drawings, Ed. May have done a heat loop once or twice, until my foreman told us it was a waste of time and materials in most cases. I found him to be right. I've Very rarely seen one installed in almost 40 years running in and out of NYC Basements. Unnecessary waste of piping in most cases. I've seen the same heat trap drawing on some water heaters and indirect over the years too. Never a problem. Mad Dog 🐕0
The diagram was for a recirculation line , The cheaper 1/2" Hobie recommended a trap on the hot water in supply . The migration of heat would cook the bulb . Did they change ? I went over to Taco years ago . Just what remembered to help out ...
Interesting T&P location, must have a 16" long temperature probe
Good spot for a float air vent though.
The probe needs to poke in to the top 1/3 of the tank.
If that valve doesn't have 100% cold shut off it would be prone to temperature creep piped like that, especially with constant circulation. During low or no use you end up with warm water at the cold port of the mix valve and it loses its mind and overshoots to tank temperature.
It's our most common tech support question, "why does my thermostatic valve over-shoot?"Bob "hot rod" Rohr
I agree Larry. I rarely see Ghost flow or unwanted hot water migration with the Holby Valves. I see many that are VERY old (piped in Red Brass) and still working perfectly. Mad Dog 🐕0
Did any of you ever meet Arthur Brown? He developed the valve. Passed on in 2007, at 99 years. A true New Yorker.Retired and loving it.0
No...but I've heard of him . Holby was on like 2nd Ave Midtown Manhattan up to a few years ago. Mad Dog 🐕0
I've always questioned the necessity of a heat trap loop on a system with constant recirculation. In fact, I don't use the trap where I know there will be near constant flow. Throw an aquastat or a timer on the pump and I add the loop.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
I think the concern is periods of no demand, as such no cold entering the valve, and the potential for hot to rise up to the valve. Not so much recirc flow?
Their manual describes the cause of creep and droop, but I don't see their piping correcting it without two valves? Looks like a 2020 rewrite?Bob "hot rod" Rohr
- 50 Industry Classes