GA124 Gauge Fickering
CGeorge
Member Posts: 4
We have a new install of a Buderus GA124 and Im not a professional boiler tech .
Whats happening with this primary / secondary loop system is some boiler flashing thats causing the gauge to flicker.
The only way Ive been able to help this issue is to replace the primary loop circ or increase the antifreeze concentration as in past we only ran about 25% . But after a couple days it comes back . I even went from a 007 to 008 and same thing happened .System pressure is always at 18-20 lbs.
Thank you in advance
No the circ is not controlled by logic and
does not have a post time set up
post a picture of your setup,
sounds like something isn't piped correctly,
how new is new and where is your contractor ?known to beat dead horses0 -
Some air trapped in the boiler passageways?
Does that boiler require an aluminum specific glycol? It’s rare to need more than 35- 40% glycolBob "hot rod" Rohr
Living the hydronic dream0