Leak , Air lock in heat system ?
RudyA
Member Posts: 14
in Oil Heating
New boiler installed , I have baseboard water heat , one zone . There’s about 25’ of the heating pipes in the slab of the house , the rest is all exposed . I have no signs of moisture coming from those areas in the floor . Randomly I come home to no heat and I have to purge the system . When I open the heat pipe loop , it’s a steady stream . When I open the valve to add the boiler to the purge I get pops of air . Then I have heat . I was told I have a leak somewhere but it can run for days with the feeder valve off and I’m maintaining 20lbs of water pressure . Why would it leak sometimes and not all the time ? Is there something else that can cause this since it’s a new installation ? Note I did install air vents to the system .
Can you post pictures of the boiler and the piping? Especially where the the pipes go into the slab.
Have you tried isolating the zone with the pipes going into the slab to see if that zone is the cause of the problem? I've seen a few cases where a leak under the slab caused the problems you described.0 -
It’s one complete loop . Leaves the boiler to circulator pump to each baseboard heater then jumps from one bedroom to next in the floor , then returns with about 10 feet in the floor . Then enters the basement . I wouldn’t know how to isolate that run besides shutting the boiler feed off and running the heat . And like I said not loosing any pressure . I’ll try to get some pics , thanks0
I will try that with the air vents . I haven’t removed the expansion tank for that test as I’m not a plumber . If you’re asking about the boiler pressure it’s set at 20 PSI .0
So those vents that were added do not solve the problem of air getting into the system ?0
And you’re right , I don’t see an air purger , the vents are just teed in0
A vertical version air Sep would press into the piping above the boiler easily.Bob "hot rod" Rohr
Living the hydronic dream2 -
Ok thanks I will definitely look into that0
If you are going to the trouble to install that air separator you might as well do it to your best advantage. The proper order for the best air elimination is to place the air separator between the boiler and the circulator pump. Then connect the expansion tank to the bottom of the air separator, and connect the water feed valve at the same location with a tee.
What do you mean when you say "...I come home and I have no heat..."? The pipes aren't warm/hot, but the boiler is? Could it be circulation?
Are you adding water because it has left the system?
Are you sure it was properly purged in the first place, or are you just taking air trapped in the boiler and pushing it into the zone?
If you can't find a leak with a thermal imaging camera, you may be sucking in air from incorrect piping as others have mentioned.There was an error rendering this rich post.
When I leave the house for work , I turn down the thermostat . When I come home and turn it back up , radiators stay cold , but I do hear the circulator pump . Then I proceed to purge the system and some air comes out of the hose . After that. , I have heat . And I don’t have to add water manually from the feeder valve . It feeds as I have the valve open to get the air out , When I close the valve the water pressure builds back up , feeder valve stops adding water Note that this air problem happens randomly as I can go for more than a week and no problem , but then it comes back daily .
Boiler temp is fine as it serves the domestic hot water as well . Only part of the heat pipe that is hot is before the circulator pump coming out of the boiler . Pump is hot also . After that the pipe is cold .0
I was told to shut this valve off when purging the system . As soon as I open this valve , the steady stream of water from the hose starts skipping with air . Seems like the air is getting trapped between the circulator pump and boiler
Are you purging through that red handled boiler drain upper right of this picture? Looks like you could but you would be purging in the reverse of the normal flow.
Yes , that’s where i connect a hose and purge it0
No I didn’t . Was told to purge it with the heat off0
How much are you setting back the thermostat. Takes some time to get high mass radiator systems heating back upBob "hot rod" Rohr
I turn it down to 60 since the weather has been nice . I’ll turn it up to 67 when needed and the radiators get hot immediately.0
try closing the air vent at the expansion tank. It looks like you installed it yourself.0
- 116 Geothermal
- 169 Indoor-Air Quality