Fostapex
eddah357
eddah357 Member Posts: 4
Anyone know how I can figure out how many BTU's 1/2 Fostapex can support. The home I moved to has 1/2 Fostapex feeding 3 rooms with standard hydronic baseboard, this zone recently froze with the extreme temperatures we had in Massachusetts.
I would like to verify total piping length and baseboard calculation to verify 1/2 can support the installed baseboard.
    hot_rod Member Posts: 27,417
    A bit over 2 gpm will be the comfort range for 1/2" pex
    Here is a 100' loop, 12 elbows, 2.25 gpm at 180F.  The flow velocity of 4 fps is acceptable.
    A fin tube system designs around a 20° delta so 20,225 btu/ hr is a reasonable number
    If you know the exact length of the loop, number of fittings, or if you have glycol in the loop, the calculator is at the PPI website.