Does the Laars Endurance EBP 110 circulator pump modulate its speed according to the flame output?
Chris Alonzo
Member Posts: 50
in Gas Heating
The voltage going to my circulator keeps changing and it even goes down to 14V sometimes, causing the boiler to kettle. I was wondering if the cause is a bad boiler control or a bad PWM (modulator) board.
Read through the manual, I don’t see any mention if the pump being variable speed
The label on the pump does it indicate VS
IT would have 4 wires is it is a 0-10vdc controlled pump. My Lochinvar has a Grundfos VS circulator m, 4 wire.
It could be a standard PSC circ controlled by a triac for speed control.
If this is the model you have?
https://www.laars.com/images/uploads/products/1117F.pdf
That is what I have. The circulator is a Grundfos UP15-42F. It is a 2 wire 120VAC motor.
Sounds like a standard circ, unless I’d shows MixiMiser which was a VS circulator, generally black in color with a much larger terminal box.
If it is being controlled by a wave chopper or triac, I don’t think you can read that output with a standard voltmeterBob "hot rod" Rohr
Living the hydronic dream1
