Gas Boiler Original 1-1/4" Supply Line Reduced to 1" and 3/4"???
rapco
Member Posts: 1
I have a gas boiler in a main house which is also heating four attached row homes.
Unfortunately, the boiler system needs to be re-piped hopefully in Pex-A oxygen barrier pipe. This is due to deteriorating steel lines originally installed in 1960.
The supply/return (S/R) lines are 1-1/4” from/to the boiler. However, the supply line is reduced to 1" and even ¾” at the end of the row homes. Also, I noticed that some of the ¾” zone valves are also reduced to ½”.
Is there an advantage or not, that the new S/R lines are 1-1/4" throughout, and also increase the new zone valves back to ¾”?
The approx. total S/R line run distance from the boiler to the last row home is about 240', total loop approx. 520', not including the 3/4" distribution lines for the registers in each room approx. 35 registers plus some slant/fin baffles.
Thank you!
Thank you!
It all depends on the flow required. The bigger the pipe the more flow. But you need to know how much flow you need to decide that0
1 inch line is good for 100,000 btu
1 1/4 is good for 125,000 btu ( maybe a little bit more)
It’s like 10 pounds of potatoes in a 5 pound bag .
So if your boiler is Over 100,000 btu on your output you need 1-1/40 -
It could be piped reverse return and the pipe size would step down like that. On a run that long, good chance is RR