Need help with American Standard GPH Natural gas Boiler
jeffa_2
Member Posts: 8
in Gas Heating
I’m stumped, I’m looking at a 50 year old American Standard Natural gas Boiler model GPH-100. The boiler is operating between 180*F and 220*F. And due to the overheating the pressure is approaching 30PSI causing the relief valve to drip.
I cannot find a high & Low limit control anywhere, I’m puzzled.
Does anyone know what controls the high and low limit on this boiler?
I will send pictures
show the compression or expansion tank alsoknown to beat dead horses0
I replaced the expansion tank with an extol #300
There has to be a high limit there somewhere or the boiler would have cooked long before this. look inside the jacket cover0
Thanks, the only cover that comes off is at the bottom for the burner only, the rest is the jacket0
I agree there has to be a high limit somewhere maybe it is built in under the jacket but I’ve never seen that before0
Thank you for the hints! I found it in the junction box where the toggle switch and the transformer mount. However, there is no adjustment, it must be factory set. I think the only fix now would be to install a new strap on Aquastat to interrupt power to the gas valve at 180*F0
Look under the white front cover or it may be behind a panel in the back or the
Nevermind!Edward Young Retired