i have a 1 pipe steam system. off of furnace one line goes to about 12 radiators and the other line of the furnace feeds only 3 radiators. For some reason, the one that feeds the 3 radiators, unless i take off valve on the 3rd floor, the one on the first floor and 2nd floor dont get hot. i was going to put in another vent on that radiator...should i do it? or see photo, not sure what this "T" is called, but will that work allowing more air to escapet? thanks
vent.jpg 492.4K

Comments

  • random12345
    random12345 Member Posts: 469
    Please post some pictures of your boiler and the near boiler piping.
  • alanm
    alanm Member Posts: 71
    here are some photos of boiler..... photo 3936...piping coming out of header-- piping going to the left handles majority of the house...piping going to the right handles 3 radiators (1st, 2nd and 3rd floor).....the piping to the far right is return . photo 3935 show the lower piping is the return and the piping above is the one going to the 3 radiators. thanks




  • random12345
    random12345 Member Posts: 469
    edited November 2022
    I'm a non-pro homeowner, so take what I say with a grain of salt. There should not be any copper in your near boiler piping. Here is an excerpt from my boiler's manual (Burnham Megasteam) that explains why:



    Does the return (far right pipe) handle the condensate from all of the radiators or just the ones supplied by the left main in 3935? Your main venting is almost certainly inadequate if the green vent is the only one you have. This should help you understand how to balance your system:

    https://heatinghelp.com/assets/documents/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-1.pdf

    I have a combination of B&J Big Mouth and Gorton #2 vents for my main venting. Works well.

    I could be wrong but the water heater vent pipe looks like it was installed backwards. The crimped end is supposed to be on the water heater side, flared end chimney-side. That's to prevent exhaust gases from leaking out.




  • alanm
    alanm Member Posts: 71
    thanks....so that Green main vent is the only vent in basement piping and it is off the "return" piping for the one long run only... (the main which feeds the 3 radiators does not have a seperate return). so besides the pipes should not be copper (should i insulate them?), should i add more vents on that 3rd floor radiator to let the air escape or what should i do? thanks.
  • pedmec
    pedmec Member Posts: 973
    @random12345 The flue is absolutely going the correct way. If it was backwards the screw head would be on the other side. Please stay on topic. Customer wants a solution to his heating problem. Not to have his boiler nitpicked for issues that ain't related to the problem. If i wanted i could find a problem with every boiler i look at.

    can you please take a full view picture of boiler and piping. it helps to have a complete picture to see whats going on
    random12345
  • alanm
    alanm Member Posts: 71
    more photos.. photo 4099--.lower pipe is the return pipnig with green main vent at the end and the pipe above that is the one that only handles 3 radiators ( 1st floor, 2nd floor and 3rd floor). photo 4098...one main pipe going to the right feeds most of the radiators in entire house..pipe going to the left is the one for the 3 radiators. photo 4101...lower is return ...upper is the one feeding the 3 radiators. thanks...again. issue is the radiators on the run where there are only 3...unless vent is taken off the 3rd floor radiator, the ones on the 1st and 2nd floor really dont get hot. the other run works fine. thanks
  • random12345
    random12345 Member Posts: 469
    With all due respect @pedmec although your comment may have been well-intended, as far as I know you're not a forum moderator. It's not your job to tell me what I can and cannot comment on. And I disagree with you. When people post pictures on here asking for help solving a problem, it makes no sense not to comment on unrelated issues if those are potentially important. In this case, he has insulation on his mains, but not his near boiler copper piping where the heat loss is substantially higher. Regarding the water heater vent pipe, I don't see how you can tell from such a blurry picture whether or not that thing is attached correctly.

    @alanm Another reason I mentioned your water heater venting is because I noticed the water heater's vent pipe appears to connect to the chimney below the boiler's vent pipe. According to NFPA 54 (National Fuel Gas Code), it should be the other way around. Whether or not this is a problem, I can't say. Not trying to make your life more difficult here.



    If possible, yes I would consider insulating the near boiler piping. Depending on how long the right main is feeding the 3 rads, the reason those rads are not getting hot may be because you don't have any main vents at the end of that main. Steam follows the path of least resistance. Simply adding more vents to those rads is probably the wrong approach. You might also want to add more main vents to the other main as well. You have a lot of radiators, so your mains are probably pretty long. That document I linked to does an amazing job of describing how to balance steam systems and was written by a pro.
  • alanm
    alanm Member Posts: 71
    thanks....so that main that is my problem that only has 3 radiators on the run and does not get hot unless i take vent off the 3rd floor radiator...where do you put main vent? not much space from the time it leaves the boiler until it goes behind the wall and up to the 3 radiators.....thanks again.
  • random12345
    random12345 Member Posts: 469
    edited November 2022
    Post some more pictures of that main, the full length of it including the end before it goes into the wall, and as @pedmec said, pictures of your boiler.
  • alanm
    alanm Member Posts: 71
    here are more photos...one correction..that one main actual make a quick turn to a radiator on the first floor....then it continues around and up thru the wall to the 2nd and 3rd floor. 4106 shows where it turns to a radiator on the first floor and then it continues (4103)...then turns to the wall (4105) and then up thru the wall (4104) and this is what goes to the 2nd floor radiator and then up to the 3rd floor.
    thanks
  • random12345
    random12345 Member Posts: 469
    Ok. In all those pictures, is the 3-rad main the top or bottom foil-covered pipe? Can you post a picture of the very end of that main in the basement? That would be my choice for where to install a main vent.
  • alanm
    alanm Member Posts: 71
    it is the top pipe. from the other photos sent...you see it come off the boiler, then split off to the 1st floor L/R and then continues on, makes another left then up into the wall...that is it. ..then thru the plaster wall to the 2nd and 3rd floor, photo attached is the one that shows the pipe right before it heads into the wall.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,202
    edited November 2022
    The easiest way to start addressing your problem is to increase the venting on the cold radiators, starting with the one on the top of the short main. You probably also have to reduce the venting on the radiators along the long main. That would "hold back'' the steam on the long main until some circulation begins on the shorter one.

    Once steam begins condensing in radiators, it draws in more steam. Thus the first to heat continue heating more and those that haven't begun to heat may be completely denied steam.

    You may also consider venting the short main, though the improvement may not be worth the work.

    As was also mentioned, the piping around the boiler has some deficiencies which further enable the problem, but you should get satisfactory improvement with venting changes.

    Switching the vents to a quality domestic product, like Gorton's, may be necessary to balance the system more precisely. Working with home store Chinese vents is often a waste of time, money and energy.

    You should also check basic other concerns like boiler run time, etc.
  • alanm
    alanm Member Posts: 71
    thanks......so should i add another vent to the 3rd floor radiator- to make it have 2 to allow air to get out of the radiator faster. as noted, when i take the vent off altogether, that is when that radiaor and ones on 1st and 2nd floor work/get hot. if so, where do i add the vent (above the existing vent) or use that "t " i saw and placed photo earlier. thanks!
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,202
    edited November 2022
    If removing the vent entirely makes the system operate to your liking, and doesn't produce noise, then the problem should be addressable to your satisfaction with increased venting of that third floor radiator or riser.

    There are several ways to accomplish this. One would be to pipe a vent on the riser before the radiator. The radiator valve would be replaced with a tee and a straight valve to the radiator off the bull of the tee. The top of the tee's run would take a nipple and a main vent. This is probably too involved, so...

    Another vent could be added by drilling and tapping a second vent into the upper part of the radiator, above its present vent, where a hot water bleed would normally be placed. Newer (1930's) radiators usually have an un-drilled boss on the casting for this. This too is involved and may be more than you'd want to tackle.

    If you've already tried the biggest vent you can find, like a Gorton D, you can tee two vents together as you illustrate. The drawback of this may be poor condensate handling with some spitting and gurgling, but that would be dependent on steam quality, velocity, and temperatures affecting production of condensate. This may only present on a very cold day in heating a cold radiator. Watch the pitch of the radiator, and make certain it pitches toward the valve. Give it a try. It may work out just fine.

    Certainly before you cut into any pipes or drill any holes, get rid of any Chinese vents and try balancing with some real ones. Working with junk parts just wastes time, work and money.

    Good luck with your mission.
  • alanm
    alanm Member Posts: 71
    thanks...i am seeing a lot of different types of Gorton vents...#4, 5, 6 and D.. any of these allow more air? thanks again...you haev been very helpful. alan
  • random12345
    random12345 Member Posts: 469
    @alanm There is no subsitute for understanding basic steam principles. Steam follows the path of least resistance. When your boiler fires, steam will rush out towards the single main vent on the left main. Once that main is completely filled and the main vent closes, it will start "searching" for the next path of least resistance. If you put bigger vents on those 3 other rads, the steam still has to push all of the air out of that second main before it can even begin to fill up the risers leading to those rads. In the meantime, some of the steam will be pushing towards the other rads connected to the first main, so you may have to slow the rate of venting on those as well in order to balance the whole system. It's not an ideal situation, and that's why the right approach is to vent the mains as quickly as possible with big vents like Gorton #2 or B&J Big Mouth. That + insulating those copper pipes, should save you money in the long run. A plumber may be able to cut into the second main and add a tee where you can probably DIY screw in some additional main vents and also add onto or replace that single main vent on the first main.





  • alanm
    alanm Member Posts: 71
    Thanks! makes sense....any special insulation needed for the copper pipes or will any do?
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,202
    Alan, the Gorton vents are made in sizes 4, 5, 6, C & D. The largest is D. Get one or two big vents on that top radiator, smaller ones on the hot radiators and you should be fine. Then you can play with the rest of the stuff.
  • alanm
    alanm Member Posts: 71
    thanks!
  • random12345
    random12345 Member Posts: 469
    I would go with Knauf pipe insulation: https://knaufnorthamerica.com/en-us/products/pipe-insulation. Find your nearest (and cheapest) local distributor and order from them. It is formaldehyde-free. Have it delivered. Or you can go with buyinsulationproducts.com/. Fiberglass is best for steam pipes. Unfortunately, it's also best to wear a respirator/gloves/suit to prevent the fiberglass from going into your lungs and sticking into your skin. At least an N95 dust mask and goggles. Armacell makes a closed-cell elastomeric foam called Armaflex, and their UT SolaFlex is good to 300F. I don't know how well it works, but the advantage is you don't need to deal with the installation headache and it's easier to cut. You can order some and see how it performs. It's such a small job.