Weil Mclain SGO with Carlin EZ gas T-Stat question.
Options
Eric L._2
Member Posts: 94
As the title states I have a Weil Mclain SGO steam boiler with Carlin EZ gas burner. Im trying in to install a vision pro 8000 th8321 but cant quite figure out where to pull a c wire from. Has anyone ever wired a smart stat to this combo before? Any advice?
0
Comments
-
There is no C-wire hookup on this combination.
We generally mount a transformer-relay unit such as an R8239A:
https://www.supplyhouse.com/Resideo-R8239A1052-40-VA-Fan-Center-w-SPDT-Switching-Action-Includes-R8222B?utm_source=google_ad&utm_medium=shopping_neutral&utm_campaign=Shopping_Neutral_LPLTV&gclid=EAIaIQobChMIrPvxps3Q-gIVQpFbCh1QMAcfEAQYASABEgJlivD_BwE
on a 1900 box in a convenient spot.
Wire your red thermostat wire from R or RH on the thermostat to R on the transformer, green to C on both, white from W on the thermostat to G on the transformer. Run the normally open relay wires outside the box through a Romex connector or bushing, then run a thermostat cable from these to TT on the primary.
This will constantly power the thermostat as long as the power is on to the boiler.Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Same concept as Steamhead mentioned, this is probably an easier installation
https://carlincombustion.com/kool-kit/1 -
Thank you both. I appreciate you sharing your knowledge. I will report back.
Eric0 -
@Robert O'Brien , how would you hook this up? The manual isn't too helpful............Robert O'Brien said:Same concept as Steamhead mentioned, this is probably an easier installation
https://carlincombustion.com/kool-kit/Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
So in the end I bought some 18/7 wire and just ran it all new. Installed a 24v 40av tranformer at the boiler and 4 wires later all seems to work fine. Left myself a few wires in case I run a remote sensor. Again ,thank you all who replied.
Eric0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements