Outdoor Reset for Peerless Cast Iron Boiler
PilotPat24
Member Posts: 104
in Oil Heating
Hey Guys,
Does it make sense to add an Outdoor Reset to a 25 year old Peerless WBV Oil Fired Boiler? Any recommendations or input would be greatly appreciated.
Thanks,
Pat
Thanks,
Pat
I added outdoor reset to my Peerless WBV-03. I already had the L7224U aquastat, so I added the outdoor reset module and sensor. You have to be careful when setting up the reset curve, you have to make sure that the return water is hot enough to avoid condensation and also make sure the stack temperature is high enough as well. You don't want short cycles.
SuperTech said:I added outdoor reset to my Peerless WBV-03. I already had the L7224U aquastat, so I added the outdoor reset module and sensor. You have to be careful when setting up the reset curve, you have to make sure that the return water is hot enough to avoid condensation and also make sure the stack temperature is high enough as well. You don't want short cycles.0
How many zones? Domestic hot water? What type of emitters.
I think it's going to be short cycle city without a buffer tank, or even better yet, a reverse indirect.
A 3 way (or 4 way) mixing valve should be installed to protect the boiler from lower temp return temperatures.
Depending on your location and winters, if you put a 140° minimum in the control, you'll probably be targeting that temperature most of the winter, so it will short cycle without a buffer/reverse indirect.
@SuperTech how did you make it with your set up? What's it look like when you open it up for cleaning?There was an error rendering this rich post.
STEVEusaPA said:How many zones? Domestic hot water? What type of emitters. I think it's going to be short cycle city without a buffer tank, or even better yet, a reverse indirect. A 3 way (or 4 way) mixing valve should be installed to protect the boiler from lower temp return temperatures. Depending on your location and winters, if you put a 140° minimum in the control, you'll probably be targeting that temperature most of the winter, so it will short cycle without a buffer/reverse indirect. @SuperTech how did you make it with your set up? What's it look like when you open it up for cleaning?
The boiler only provides heat. 2000 sq ft house
Slant Fin Emitters
I am on Long Island, NY
I'll take a picture of my current setup the next time I am at the house.
Pat0 -
captainco said:The important part of boiler reset is to bring the pump on and allow the water to circulate before the burner comers on. If this is done the return water can be as low as 110 degrees. Using at least a 20 degree differential should be the minimum.
110 degree return water temperature isn't an issue with condensation?0 -
STEVEusaPA said:How many zones? Domestic hot water? What type of emitters. I think it's going to be short cycle city without a buffer tank, or even better yet, a reverse indirect. A 3 way (or 4 way) mixing valve should be installed to protect the boiler from lower temp return temperatures. Depending on your location and winters, if you put a 140° minimum in the control, you'll probably be targeting that temperature most of the winter, so it will short cycle without a buffer/reverse indirect. @SuperTech how did you make it with your set up? What's it look like when you open it up for cleaning?1
SuperTech said:STEVEusaPA said:How many zones? Domestic hot water? What type of emitters. I think it's going to be short cycle city without a buffer tank, or even better yet, a reverse indirect. A 3 way (or 4 way) mixing valve should be installed to protect the boiler from lower temp return temperatures. Depending on your location and winters, if you put a 140° minimum in the control, you'll probably be targeting that temperature most of the winter, so it will short cycle without a buffer/reverse indirect. @SuperTech how did you make it with your set up? What's it look like when you open it up for cleaning?0
Never have had any condensation problems with 110 degree returns.0
captainco said:Never have had any condensation problems with 110 degree returns.
That's great to hear! Why does it seem from what I have been reading that some people don't recommend not having return water being less than 140 degrees do to condensation?0 -
captainco said:That is an old wives tale from poor equipment setup Water heater have no problem taking on 50 degrees makeup water without condensation. Condensation is caused by improper firing or improper venting, not return water temperatures.0
Best practices say that the boiler needs to be above the dew point of the fuel with 10 minutes of running. Dew point depends on the CO 2 content of the flue gas.
For fuel oil that “industry” number has been a “safe” 130F
Check with the oil guys here, I would not run an oil boiler with 110 return temperatures, continuously without knowing and confirming how the burner is setup.
Agree. What might that problem be?captainco said:If it takes up to 10 minutes for a boiler to reach dew point there is definitely something wrong with the equipment operation
Underfiring, wet flue, restricted flue, excessive house leakage would be some of the leading causes.0 -
Any recommendations on a particular outdoor reset for this application? Much appreciated!0