Stumper- can't get boiler CO ppm down in flue- ideas?
CarissaDiMuccio
Member Posts: 1
in Gas Heating
Smith CO. boiler 140,000 BTU natural gas
CO in flue 1400 ppm and not budging after performing everything we can think of;
1. Have cleaned/brushed out burners and HX, and ppm isn't dropping.
2. Took top off boiler for more thorough cleaning.
3. Verified we have correct manifold gas pressure, proper draft, and proper combustion air.
4. Verified CO measurements with a 2nd combustion analyzer.
5. Manufacturer had us clock gas meter to verify boiler is is not over firing and operating @ correct amount of BTU's, and it is well w/in range (~132,000 BTUs).
We've never run into this before where the CO in the flue wouldn't budge. Any more ideas?
Usually it's mis-aligned burners. I can't think of anything else to check. If it were a furnace, cracked heat exchanger. Everything is sealed back up correctly, no leaks? Any CO detected outside/around the boiler? Any rollout?
Draft hood?There was an error rendering this rich post.
steve ask the important question. Does it have a drafthood? What is your O2 and flue temperature and draft? Are you sure the CO stopped at 1400 ppm or did you just stop testing? Burner alignment or bad burners would be the only other reason if your O2 and CO are stable.0
How did you confirm there's enough combustion air?
Happened to me once and I was getting all these weird numbers. My meter was set to nat gas fuel and the owner pointed out to me that it was a propane sys. Duh! Is the meter set to the proper fuel type and recently calibrated?0
you stated you verified you had the correct draft. where did you take this reading and what was it? if the captain is here that'll help him help you0
try cutting the gas pressure slightly and see if the CO changes. If it doesn't change at all your tester may be bad0