Tekmar Outdoor Reset or Internal Temperature Sensors for 14 Unit Apartment Building

Options
Hello,

I've searched for posts regarding Tekmar outdoor reset vs internal temperature sensors, and all seemed to be focused on single-family homes, so hoping to get some feedback on its use in an apartment building.

I live in a 14 unit condo building (4 stories, brick) that has steam radiators with a central boiler. Currently there is one thermostat on the top floor in our central hallway that controls the furnace. It works but isn’t great. Either the furnace doesn't turn on when the units are chilly or it runs continuously for the entire "home" cycles. We are considering either putting remote sensors in a few units and letting an average temp trigger the furnace or a Tekmar with outdoor reset to control everything.

If anyone has experience with either system in an apartment building, I would like to hear how it has worked.

Thank You

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,520
    Options
    You will find it difficult or impossible to keep everyone happy.

    Before you do the control thing it would be best to have the system serviced and cleaned and air vents installed/adjusted and balanced.

    You can add all the controls you want, but if the system doesn't work well controls won't fix it.

    Once you have the system running as good as it can, then add some controls.

    I would use and outdoor air lockout to shut the boiler down at 55 degrees (adjustable) and the thermostats (maybe 4) to call the boiler on on an average temperature
  • mattmia2
    mattmia2 Member Posts: 9,637
    Options
    Is it 1 or 2 pipe? Individual controls like TRVs at each radiator could possibly work here. Isn't this application like Heattimer's whole business? TRVs and steam are challenging but I'm not seeing 14 tenants agreeing on a single temp even if there was some way to balance it which there isn't because of varying gains and losses with changes in things like weather, occupancy and usage, and sunlight.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,834
    edited April 2022
    Options
    Is the "central furnace" a boiler that makes steam or hot water? Outdoor reset will not work with steam. It will work with a hot water boiler.

    I have had experience with several multi-tenant buildings that have a common boiler with a single thermostat. The most cost efficient job I remember was a large 3 story Victorian home that was converted to a bed and breakfast. I installed individual thermostatic radiator valves on most of the radiators in the building and installed the thermostat in the coldest room in the building. This would cause the rest of the rooms to overheat if all the radiator valves were open. Each tenant or guest could adjust the valve on the radiator to a number that was comfortable for them. Once the room was comfortable the thermostatic valve would close, without the need for any electricity or wiring, and allow the hot water to circulate to other rooms.

    If the coldest room ever was hot enough to satisfy the thermostat, the boiler would shut down. (this never happened before the TRVs were installed.) On one project, the owner saved over 1500 gallons of fuel oil, that first year of operation, after the TRV install. That savings paid for the entire job in 2 heating seasons.

    I added ODR in the following years and there was even more savings.

    If you have Steam Heat you can use TRVs designed for steam radiators. They go on the air vents if you have a one pipe steam system. Read page 20 of this text I used to use for teaching Hydronics. http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdf

    Mr.Ed

    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
  • Steamhead
    Steamhead Member Posts: 16,834
    Options
    @nziegler , this is the Tekmar control you need:

    https://www.watts.com/products/hvac-hot-water-solutions/controls/boiler-mixing-controls/279/279

    We have several buildings using this control, as well as its predecessor the 269. As long as the systems are in good shape, as @EBEBRATT-Ed says, the 279 will do what you want.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting