Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Hydronic boiler controls

Hey guys I wanted to know what this component is on this Weil-McClain 140000btu hydronic boiler. This piece is where I believe an air separator should have been because the system doesn’t have one. Instead this is about 20”


downstream of the expansion tank on the supply piping. I’ll also add a few pics of the boiler/piping itself.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • hot_rod
    hot_rod Member Posts: 25,006
    That is a swing check valve. A flapper inside slides down when the circulator stops tom prevent unwanted flow
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,703
    edited December 2021
    Flow check valve

    And if you only have one zone and no domestic hot water from the boiler you don't need it
  • neilc
    neilc Member Posts: 3,024
    is that expansion tank supported?
    or just dangling at the top of the 1/2 inch copper?
    please support me
    known to beat dead horses
    HVACNUT
  • GeoKnight
    GeoKnight Member Posts: 6
    neilc said:

    is that expansion tank supported?
    or just dangling at the top of the 1/2 inch copper?
    please support me

    You cant see it but the horizontal pipe it’s connected to it clamped to the floor joist.
  • GeoKnight
    GeoKnight Member Posts: 6

    Flow check valve

    And if you only have one zone and no domestic hot water from the boiler you don't need it

    So it has about 5 baseboards with no zoning they all branch from the main poorly insulated pipe you see with no domestic water zoning. So I suppose I can put an air separator in place of that?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,703
    Maybe they had domestic hot water off the original boiler but with only one zone and no DHW off the boiler you don't need it

Welcome

It looks like you're new here. Sign in or register to get started.

Welcome

It looks like you're new here. Sign in or register to get started.