Honeywell R7284 -- Hard Lockout -- No Ignition
silent_strings
Member Posts: 2
in Oil Heating
I'm at my mother-in-laws and their oil burner won't start -- It's a Beckett burner, the model number ends with a 'G' but the rest is rubbed off. I'm a fairly competent handy-man type, but I'm also British and we don't really do oil burners, so I'm kinda clueless right now. The Honeywell unit is showing Hard Lockout (previously with 'CALL SERVICE' but I reset it), and the errors for the last 6 cycles show 'NO IGNITION' (the next error is thousands of cycles ago).
Now, the Honeywell troubleshooting info gives me a series of steps:
1) Check that the manual shut off valve is open.
- No idea where that is
2) Check that the burner motor is spinning and the pump is generating adequate pressure.
- There's a motor-sounding noise during ignition, and the pressure meter on the boiler doesn't get above '5' (it may have shifted a little or I may have wobbled and been optimistic that it was moving, I'm assuming that's solely for the water pressure but I don't see another pressure-based readout anywhere)
3) Check the condition of the nozzle and replace if necessary.
- No idea where this is or whether I'd be sure what a worn one looks like
4) If a valve is present, check for proper operation. - No idea where this is, either
5) Check burner adjustments (refer to burner manufacturers instructions)
- You get the picture. Also, this is the one thing that even if I found it, I wouldn't go fiddling if you paid me.
So, 3 questions: 1, if it is the lack of pressure, what does that indicate? 2, if it's not that, where is the manual shut-off? 3) if neither of those things pays off, how do I get to the nozzle and/or valve, and would I be advised carefully checking and possibly cleaning them? I'm not about to replace anything, but anything I can do to avoid having to pay for the tech to come out, I'll do.
Thanks for any help you can offer!
1
UPDATE
Checked the wiring, there's nothing connected to the Valve contact and nothing loose so I guess that answers that question.0 -
How much oil
is in the oil tank?
If there is oil in the oil tank, you need a technician to come out. If there is no oil in the tank, you need oil and possibly a prime and start depending on how the tank is piped to the oil burner.0 -
Having same issue did you ever figure it out?0
Unit reads "Hard Lockout". Furnace blowing but no heat. Plenty of oil. Pressed red button...no change. What should I do?0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
