I have a 2003 Burnham Revolution propane fired boiler that is having an intermittent shutdown issue. I am wondering if anyone has some suggestions on what could be causing this and how to isolate it, as it is intermittent.

The system has 4 heat zones each with its own circulator pump. A Taco Controller drives the pumps and the 4th zone is for a heating a domestic hot water holding tank.

The problem has occurred 2 times within the last month. There is a call for heat, the circulator pumps turn on immediately and the boiler fires on shortly after that. As it is running for a time it will suddenly shut down and the boiler will not come back on. The zone(s) are still calling for heat and the circulator pumps at this point are just moving cold water. I can get it to restart and run normally again if I de-power the entire system with the main breaker.

Here is some additional background, In the summer of 2020 something similar occurred when the hot water tank was calling for heat. I was able to get it turned back on by tapping on the Honeywell 8148E Aquastat control box. In doing some research I found these units were known for having some cold solder joints on the circuit board. Sure enough on disassembly I found a couple. I touched them up and the issue went away. Tapping this time did not work.

I purchased this house in 2018 and have never been impressed with this system. I always thought it consumed excessive propane. The building inspector who looked at the house just before it was purchased noted that the baseboard radiators took a real long time to warm up and thought it may have been caused by coagulating antifreeze in the system, which never had been changed. The previous owner had the system serviced, cleaned, tuned and flushed before the closing. It really didn't help.

More research did find the circulator pumps are installed incorrectly. Per the Burnham Installation instructions they should be on the supply side, mine are on the return side. This is setup this way as this system has a variable speed internal mixing circulator that pulls water from the heating loops and feeds it into the boiler to heat it up. When the boiler is cooler the pump runs very slowly, as it heats up the water it speeds up to mix more hot water into the loops, eventually it is supposed to run at full speed. Apparently with the circulator pumps on the return side causes too much head pressure and the external circulator pumps are fighting the internal pump. I never changed them as I couldn't get a clear consensus that I would pick up much efficiency vs. the cost of making the change.

Lastly about a month ago on a cold morning I watched the system come on and noticed the small VS3000 control board that controls the internal pump speed. It has a LED indicator that tracks the speed of that pump. It blinks slowly, once every 2-3 seconds, at slow pump speed, and it increases as the temperature increases and eventually it stays on fully with the pump at full speed. I watched this for about an hour, the boiler was definitely hot, but the pump always stayed at slow speed. More research, there is a thermistor which feeds the VS3000 control board temperature data. It is supposed to sit on the exit pipe from the boiler, mine was hanging in the air. Probably was held by a nylon ty-wrap that broke overtime. I reattached it and now the pump actually went to full speed. I am hopeful that this may have been the issue all along for the radiator heating issue.

Soon after I did that I had the 1st shutdown situation with a 2nd one yesterday.

Sorry for the long message but wanted to provide as much info as I could.

Any insights or suggestions are greatly appreciated .

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,551
    Options
    Really hard to tell. Usually this type of boiler would fail on start up, failure for the pilot to light, failure of the flame sensor etc. But you said it fails after start up.

    I would take the flame sensor out and clean, inspect maybe replace it those are common to fail. A tech with a combustion analyzer to check the flame if that doesn't work and he should check the flame signal from the flame sensor. Make sure the pilot burner & flame sensor are grounded back to the flame sensing control. The flame current usually travels through the grounded metal bact to the control

    Other than that inspect everywhere for loose wires. Sometimes in a damp basement the wire plug on connectors will oxidize. Disconnecting and reconnecting the wires will clean off the oxidation
  • HVACNUT
    HVACNUT Member Posts: 5,843
    Options
    What's the temperature setting on the L8148? Is the boiler making the set temperature and going off on limit, or does the boiler go cold?
    If flame drops out before limit then you'll need an electric meter and a manometer to check the pressure switch. 
  • lp20th
    lp20th Member Posts: 11
    Options
    Thanks for the responses.

    I believe the boiler was operating for quite a while before it shut down. During the last shutdown occurrence I saw the boiler operating with two zones, one heat and one domestic hot water zone, calling for heat. About 4 hours later I check it again and the boiler is off, the pipes are cold, slightly warm at best, and both zones are still calling for heat with their respective circulator pumps still running. I power it all down and power back up and it operates normal again. To my amatuer eyes, I see what I think is a good blue burner flame through the observation port. Maybe I need to check some things on the ignition module?

    The L8148E is set to 210F. This is the manufacturers spec and I believe has to do with optimizing the boiler water blending system I described earlier. Unfortunately the temp gauge is no longer functioning so I can't quickly see what the water temp exiting the boiler actually is.

    Maybe its pressure, maybe its temperature, maybe its flame related. It's tough on intermittent problems unless you catch it in the act.
  • JUGHNE
    JUGHNE Member Posts: 11,067
    Options
    Zone controls and pumps do not know if the burner is on or not.
    I would assume you have a boiler firing problem.
    The flame sensor is always the first (and cheapest) suspect.
  • lp20th
    lp20th Member Posts: 11
    Options
    I wanted to share this in case it is is useful to someone else having a similar problem.

    I finally had a re-occurrence of this issue while I was standing next to the boiler. The shutdown is happening on its attempt to re-start the boiler during a call for heat.

    I was watching the operation and initially there was just one zone calling for heat. When the aquastat was hitting the high limit its was shutting down the boiler as it is supposed to and the circulators continued to operate. As the aquastat saw the boiler temp fall below the high limit the boiler would restart and the heat call was still there. It worked great for a few cycles, then a 2nd zone had a call for heat while the high limit was satisfied and the boiler was off. The boiler temp dropped and there was an attempt for the boiler to re-start. This time the relay in the aquastat energized and immediately de-energized. While in this state I took some measurements and found the the 24 VAC coming from the the Taco SR504 was not feeding into the Aquastat and neither was 120 VAC coming into the boiler, which also is sourcing from the Taco. Next I used the highly scientific method of tapping on the Taco box and I now could control the on/off state of the boiler by tapping on that box.

    Inside the Taco SR504 are a line of relays for the zone circulator pump control and for feeding power to the the boiler. They are socketed which is a nice feature for replacement. I reseated the relays and everything is working again but I am going to watch for another failure. Tapping on the box no longer has any effect on the operation. So it could be that simple, or maybe one of the relays is going bad, which a simple enough to replace, a cold solder joint on the circuit board or a loose connection somewhere. I did find where someone had an issue with a Taco control and it turned out to be the a loose fuse clip on the circuit board, but I don’t see that here. Not sure if the 2nd zone calling for heat was coincidental or not.

    So whether its truly fixed or not, time will tell, but at least now I believe I believe I have the problem isolated at its source.
  • HVACNUT
    HVACNUT Member Posts: 5,843
    Options
    A cube relay being loose will do it.
    The newer Taco zone panels use non replaceable relays that are secured to the circuit board. 
  • lp20th
    lp20th Member Posts: 11
    Options
    As I think about it, the Taco Control is mounted to a studded wall. This past summer some work was done on the outside of that wall about 8 feet away. There was significant vibration from drilling and pounding. Not too long after that the 1st occurrence of this issue showed up. At 1st it would show up once every 2 months or so. As the heating season started it became more like every 2 weeks.