Hydronic boiler controls
GeoKnight
Member Posts: 6
Hey guys I wanted to know what this component is on this Weil-McClain 140000btu hydronic boiler. This piece is where I believe an air separator should have been because the system doesn’t have one. Instead this is about 20”
downstream of the expansion tank on the supply piping. I’ll also add a few pics of the boiler/piping itself.
That is a swing check valve. A flapper inside slides down when the circulator stops tom prevent unwanted flowBob "hot rod" Rohr
Flow check valve
And if you only have one zone and no domestic hot water from the boiler you don't need it
So it has about 5 baseboards with no zoning they all branch from the main poorly insulated pipe you see with no domestic water zoning. So I suppose I can put an air separator in place of that?EBEBRATT-Ed said:Flow check valve
Maybe they had domestic hot water off the original boiler but with only one zone and no DHW off the boiler you don't need it0
- 87.2K THE MAIN WALL
- 119 Chimneys & Flues
- 164 Indoor-Air Quality
- 75 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.6K Strictly Steam