Internal Boiler Circulator - primary / secondary piping
Options
mtbllp
Member Posts: 1
Weil McLane GV-5, Series 1 boiler has an internal circulator pump. I am setting up primary secondary piping. Zones include air handler, baseboards and indirect water heating.
Is the internal circulator pump all that is necessary for teh primary loop? Or, is a second external circulator necessary?
Thanks
Is the internal circulator pump all that is necessary for teh primary loop? Or, is a second external circulator necessary?
Thanks
0
Comments
-
The boiler pump will take care of the primary. For your secondary circuit, if you are zoning with zone valves, a second pump is necessary. If you are zoning with pumps, there will be one pump per zone.

8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Is it a GV 90 plus-5? The manual shows how much pump capacity you have to work with.
if it is an older GV, some of those had a circulator inside for return temperature protection, and still requires a system circ.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 128 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements