Lochinvar Noble Combi 199--- very little hot water

Options
TBL
TBL Member Posts: 1
edited December 2021 in Domestic Hot Water
Brand new installation of Lochinvar Noble Combi, propane, even though the temp DHW is set above average temp, we are getting very little hot water before it runs cold, 10-12 seconds worth. Before installing the recirc loop with aquastat the volume of hot was plentiful. Of course that was before the space heat season triggered that demand on the unit too. Advice? Yes, if we turn off the tap for a minute or two it will warm up then be hot for another 10 seconds.

Comments

  • hot_rod
    hot_rod Member Posts: 22,157
    Options
    could be a cross connection in the piping?  Is there a thermostatic mixing valve in the piping

    Does the boiler continue to run when hot water is flowing?  Could bet the recirc pump is closing the flow switch that triggers the boiler and diverter valve inside 
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tom_133
    Tom_133 Member Posts: 884
    Options
    You may need to post some pics of the recirc loop install. More than likely thats the culprit
    Tom
    Montpelier Vt