How Is This Looking? Tips/Suggestions?
RyanNYC
Member Posts: 9
I have a one-pipe system on a Slant Fin GXH series.
I have a lot of interest in steam wanting to learn the RIGHT way. Tips and/or suggestions on this photo.
I reckon I should insulate the piping
Make sure the header is at least 24" above the water line.
How's the steam quality? Any problems?Just another DIYer | King of Prussia, PA
@Hap_Hazzard The steam quality seems okay. I recently just replaced some vents on the header and the radiators which helped out dramatically. The one thing I think I'm unsure about is the lower portion of the hartford loop where the drain cock is. The make-up water is piped there as well.
I also added 8 way chemical earlier this year.0 -
1
https://heatinghelp.com/store/detail/we-got-steam-heat-a-homeowners-guide-to-peaceful-coexistence
2
https://heatinghelp.com/store/detail/the-lost-art-of-steam-heating
3
holidays are here , , ,
we've seen far worse,
looks good enough,
cept,
hartford loop should be a close nipple,
safety valve should pipe down to 6 inches from floor,
are you having issues?
insulation is your friend, all steam carrying pipes, including at the boiler,
known to beat dead horses0 -
You will get some flak from others about that nipple between the Hartford Loop and the equalizer. It should be as short as possible because water can sit on the horizontal surface and create problems.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
@Alan (California Radiant) Forbes I can see how that could potentially be an issue, thanks for that, noted.
I think you're confusing the header with the steam main. The header is the horizontal pipe that goes from the supply riser to the equalizer. Make sure the bottom of that pipe is at least two feet above the water line.RyanNYC said:The steam quality seems okay. I recently just replaced some vents on the header and the radiators which helped out dramatically.
@Hap_Hazzard
Just eyeballing the sheet rock on the wall looks like he is well over 2'. Hartford loop needs fixing though0 -
@EBEBRATT-Ed Fix the Hartford loop in what way ?0
That ~6" horizontal nipple should be a street ell or a close nipple, it is a place for water to collect and meet steam and cause hammer.0
- 117 Geothermal