Pressure Rise During Boiler Firing Up
allthumbs
allthumbs Member Posts: 10
My Utica hydronic boiler for all its years in operation has always maintained 12 lbs pressure either cold or fired to 180 degrees. Now, with a new expansion tank, same size and brand, the pressure rises from 12 lbs cold, to 20 lbs at 180 degrees. I realized the plumber had mounted the new expansion tank water chamber down. Extrol rep. indicated that there is a chance of air getting trapped in the water chamber with water chamber down. I called back the plumber, and had him redo the fitting to permit mounting the tank with air chamber down. While the tank was off during the redo, I rechecked the tank pressure, it was still at 12 lbs. Changing the tank position didn't help, the pressure is still rising to 20 lbs with the boiler fired up. I don't rely on the water pressure regulator to get to 12 lbs cold fill. I watch the gauge, and when it reaches 12 lbs, I turn off the water inlet valve to the boiler. I'm wondering if the fact that the boiler was kettling for the last couple of years has anything to do with this problem. After refilling the system, the kettling stopped. I thought that's a good thing, indicating the debris got flushed out. On the otherhand, what if the refill forced the debris into some of the heat exchanger channels, causing the problem. BTW system is heating just fine.
    EdTheHeaterMan Member Posts: 11,559
    edited November 2021
    I wonder what the chances are... could the gauge have been stuck on 12 psi for all those years? With the gauge stuck a 20 psi boiler might still read 12 psi.
    Does the boiler work? Are you getting proper heat? Is there any water leaks from the Pressure relief valve? Are there any unusual noises?
    If you can answer NO to all these questions... it ain't broke! Dont fix it! 20 PSI is just fine!
    kcoppunclejohnEBEBRATT-Edallthumbs
    mattmia2 Member Posts: 15,547
    Maybe the "kettling" was a huge air picket trapped in the boiler causing the system to act like it had a much larger than necessary expansion tank.
    allthumbs
    EBEBRATT-Ed Member Posts: 19,529
    @allthumbs
    I agree with @EdTheHeaterMan
    a rise in pressure from 12-20 when heated seems normal
    allthumbsEdTheHeaterMan