Manifold for Navien to zone panel assembled and ready to be pressed. Any thoughts before doing so?
JohnJr
JohnJr Posts: 14
edited October 2021 in THE MAIN WALL
Updated picture of manifold all pressed. I have the supply line sloping down to the zone panel, and the return line sloping up at an angle. What's everyone think?
  • PC7060
    PC7060 Posts: 1,956
    edited October 2021
    How are you supporting the tank?
    can’t tell if you have a shutoff between in and the air removal device.  If not I’d add one.
  • JohnJr
    JohnJr Posts: 14
    edited October 2021
    @PC7060 it's supported in the back by a metal hangar strap connected to the zone panel frame. The air removal device is the brass cylinder looking object left of the top pressure gage on the panel. There is a shutoff valve left of that and the two yellow lever shutoffs closer to the top with fill and purge valves. I am also able to disconnect the manifold with it's 4 disconnects (2 on the boiler, 2 on the zone panel).
    PC7060
    hot_rod Posts: 28,329
    The backflow preventer, can it be mounted vertically?
  • JohnJr
    JohnJr Posts: 14
    @hot_rod yes for this particular WATTS model, vertical installation with flow up is okay.
  • PC7060
    PC7060 Posts: 1,956
    edited October 2021
    The prefab manifolds with shutoff seem
    like nice time savers
  • jad3675
    jad3675 Posts: 128
    Anyone have concerns with the taco zone box being mounted below water?