Burner Issues
Options
Bomba
Member Posts: 28
Hi all,
I’ve had one burner out on my Utica steam boiler for a few years now. I think it’s time to fix it before the cold comes. Attached is a picture. Anyone know what I should do to fix this issue?
I’ve had one burner out on my Utica steam boiler for a few years now. I think it’s time to fix it before the cold comes. Attached is a picture. Anyone know what I should do to fix this issue?
Thanks!
0
Comments
-
Remove the burner and check the orifice at the manifold. Typically, a spider in residence has made its egg casing there during the summer months.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0