Biofuel fuel in tank?? What is this?
Came home to a cold shower a found the burner out. I’m a licensed and well seasoned oil tech so I got into it and when I purged the burner this dirty yellow oil mixed with red #2 came out.
Will update tomorrow
Ya the tank is inside. The oil line is at the floor about 8ft long.I’ve had to drain water from tanks before and it always looked a dark color.Gonna try and draw off as much as I can from the tank0
Yup, water. I just went thru this with a customer and an underground tank.
If it's gravity flow (and no OSV), I'd draw it off at the Tiger Loop until it's clear. Then I'd replace filter, strainer, nozzle, drain the flex lines & do a full combustion test.
Then I'd treat each tank for a whole season and check the filter next summer. Fill the tank when the heating season is over.
You could've also had a bad load.
You shouldn't have to purge it with a Tiger Loop. But the obvious problem is the burner won't burn water.There was an error rendering this rich post.
@PhilDavid
Get some of that water testing paste at you oil burner supply house and check your sample. Try and find out how water could get in the tank...that looks like a lot to get from condensation.
Talk with your oil supplier0 -
Once properly blended, biodiesel doesn't separate from #2To learn more about this professional, click here to visit their ad in Find A Contractor.0
Appreciate the feedback.
Yes it does look like strawberry quick in the tigerloop.Right from the tank I removed about 3 gals of this stuff. Replaced nozzle strainer and filter. And cleared the tigerloop and lines. It fired up so I let it run until the indirect was satisfied (so wife could shower) but then turned it off. I’m going to fire it back up after work and do a combustion test.Definitely going to call the supplier. It just doesn’t seem right.1 -
STEVEusaPA said:Yup, water. I just went thru this with a customer and an underground tank. If it's gravity flow (and no OSV), I'd draw it off at the Tiger Loop until it's clear. Then I'd replace filter, strainer, nozzle, drain the flex lines & do a full combustion test. Then I'd treat each tank for a whole season and check the filter next summer. Fill the tank when the heating season is over. You could've also had a bad load. You shouldn't have to purge it with a Tiger Loop. But the obvious problem is the burner won't burn water.0
I thought the HotShot would emulsify the water, maybe it was too much for the amount of HotSot you used?
A RACOR 500FG fuel filter would collect all that water and dirt for you.
The FG model has a stationary vanes which create a centrifugal flow of fuel which spins the water and dirt out of the fuel and collects against the clear polycarbonate bowl where it settles down to the bottom of the bowl.
The clear polycarbonate sediment bowl allows you to monitor the amount of water and dirt it collects and then you can manually drain it (and not lose the prime thus avoiding the line becoming air bound) into a bucket or coffee can, to get rid of the dirt and water by dumping it in kitty litter and take all the guess work out of it.
The 10-micron cartridge filter is good for 10,000 gallons of filtration.
Hot Shot, Heet or 9-1-1 would not take care of all that water.
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
