Cause of heavy corrosion - mystery
Cookhigheffhaus
Member Posts: 7
I had a new HE boiler installed in 2016 in my home. Since then I've had some troubling corrosion problems. First I noticed on the 110V elec supply (BX cable) the metal sheathing on the cable (Al) is completely dissolved in about a 3 in long section. There is a semi clear goo where the metal cladding had been.
Also have serious corrosion near one of the boiler circulator pumps where steel nipple connects to brass check valve (then another steel nipple and elbow into 1" copper). Saw today that connection at the valve now has a small drip.
One thing I noted inside the boiler (Burnham Alpine 150kBtu) is it looks like the ignition wire to the main igniter was pinched under a flange during construction. I could not move it. Having worked on high voltage systems in a past life, I know stray high voltage can do strange things and if the insulation is slightly compromised I could have voltage leakage.
Any other thoughts on these corrosion issues (and I don't live near a body of salt water)?
Condensate leaking back in to the armored cable.
Is the nipple leaking slightly or is the system leaking such that it is having makeup water added?0 -
The ignitor cable, if grounded even somewhat, would not deliver the spark needed to light the burner. And it is only hot when the ignition cycle is active.
Matt may have the answer with condsate leak, that is quite corrisive to most things except plastic, PVC etc.0 -
Also details about what type of heating distribution, is it radiant, radiators, air coils? If any plastic, PEX tubing was used it needs to be hydronic specific with an oxygen barrier.
Every picture tells a story.Bob "hot rod" Rohr
What is the water quality in the sys? Anti-freeze? Post some pics.0
"the metal sheathing on the cable (Al) is completely dissolved in about a 3 in long section. There is a semi clear goo where the metal cladding had been."
Do you have any pictures of this?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Sorry posted pics in response to DM. Here they are -- still looking for clues. Regarding the other questions: Boiler serves rad floor; steel wall radiators (runtal new); coil in forced air system. Filtered water filled - no A freeze. Pex Oxy barrier and copper piping. Leak is ~ 1 drop per week.
Arrow in pic shows pinched ignition wire.
@mattmia2 makes a good point about a concrete tie.
Aluminum flex won't deal well with concrete if their is any moisture.
The other two piping leaks should be fixed, there is a flange right there so it's an easy fix as well as the ignition wire0 -
While the repair is being done on the strainer, rotate the circulator flanges. The motor should be horizontal.
Replace and reroute the B/X cable. That's scary.0 -
Is that "strainer" actually a swing check valve?
I see the bolt that might hold the swing gate in place.
It should remain in the position it is in now.
But yes the motor shaft should be horizontal.0 -
The s as aluminum flex is intake air, I hope?
the leak at the pump may just be a bad thread connection.
The check is oversized, too close to the pump, and the wrong type for Hydronics.Bob "hot rod" Rohr
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar