Bad taco relay 24v?
mattyc
Member Posts: 45
What are the steps to troubleshoot the 24v side of a taco switching relay? Just moved into new house with a single zone oil boiler I bought and installed a taco 2 zone switching relay ( I plan on installing an indirect tank for zone 2) I wanted the relay to utilize the common terminal for my Honeywell lyric stat..I ran brand new wires as well directly to the boiler controls from the thermostat. After installing the thermostat, it would not turn on...I figured it just got banged around and broken while in the process of moving and I know the lyric stat is not the best in Honeywell’s lineup...so I buy a new thermostat and I get the same results. After some time with a meter I’ve established the thermostat wire has continuity and I have 24v between 24v and common terminal but the thermostat will not even light up. Am I testing wrong? Low voltage issues have always been a week point for me. Also to be noted I still have the thermostat wired to the triple aquastat “TT”with the exception of the third wire to the switching relay common terminal Thanks for any input
Where did you pick up the common for the thermostat ? Do you see the terminal block top left in Alan's diagram , common on bottom terminal is were you pick it up. Power off when wiring ...
R and W on the thermostat connect to TT on the aquastat, and Common on the Switching relay connects to C on the thermostat?
What's connected to R and W on the switching relay?
Do as in the diagram above. But do the XX thing Only after you install the indirect.
If you're currently using a tankless coil and running out of hot water, wire in ZR,ZC instead, between the switching relay and the aquastat. It's line volt switching there so use 14 gauge wire. It should be on a 15 amp circuit. If for some reason it's on a 20 amp breaker, use 12 gauge.
By using ZR,ZC, if the boiler temperature drops below the low setting, it will shut off the heating circulator(s) in order to help provide enough domestic hot water.
Once you install the indirect, remove ZR,ZC and use XX.
Yes the boiler turns on as usual since I put the old thermostat that came with the house back together wired to TT on the triple aquastat and when I tried wiring my wifi therms I picked up the commin from the terminal block on the top left. I’m thinking that the terminal block on the top left is bad? But I may be testing it wrong. I’m not sure0
Is the circulator wired to the aquastat? It needs to be wired to zone 1 on the Taco relay as well.
The 24v terminal block is not bad.0 -
@HVACNUT thanks I’ll try that. So my current situation when trying to wire my wifi stat that is, my circulator and Rh&W are wired to the triple aquastat and I was just wiring common on the thermostat to common on the switching relay...I was being lazy by not wiring everything to the relay but I assumed no reason why it all wouldn’t work. I don’t quite understand why it wouldn’t but I’ll wire it all to the relay with Zc Zr for my tankless and see what happens. Thanks0
If you swapped the wires at TT it might work, but it's not right.
You're dealing with two separate power sources. A transformer in the Taco and a transformer in the aquastat. They're butting heads at the thermostat and that won't make anyone happy. When things are idle, you'll get a back feed through the transformers coils and pretty soon it won't be pretty.1 -
@mattyc If your using a tekmar stat, might I direct you to this?
https://www.watts.com/products/hvac-hot-water-solutions/controls/zone-controls/302p/302p
Mike B (tekmar)0 -
@Mike_Breault I think I’ll go that route in the future for sure once I zone my house better and add radiant. Thanks0
@mattyc Anytime and thank you for considering us.. I think you'll like it, a couple nifty features athat I really like is you can mix and match pump and Zone valve controllers, and the ability to leveraqe the away feature.. use 1 wifi stat like the 561 and low cost 519s, when you put the wifi in away, it triggers the 519's. low cost wifi system for Home / awat mode.
Be well0