Honeywell ML7421A1032
hvacPaul
Member Posts: 1
I have this valve. 24 volt supply
0-10volts dc control to open and close the valve
I found space over heating when I got here. Checked valve and found in mid open position. With no call from control system. I cycled valve a couple times , but always goes back to mid position. I checked the jumpers on the W3 and W4 spaces. They seem to be set correctly.
Am I missing something ? Or is the valve no good
thank you
thank you
Make sure the selector plugs are in the right spot. Did you check the signal? if it is in mid position you should have a 5 volt signal.
Selector has to be set up right for 0-10vdc, 2-10vdc, or 4-20ma
I would unhook the signal wires to it and hook up a signal generator if you have one and see if that drives it back and forth0