Quantity of condensate from condensing appliances?

Options
Does any one have (is there a reference) for the quantity of condensate from a condensing boiler, water heater, furnace?

(just is case some state review asks for sizing information on the condensate pump)

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,181
    For every 100,000 btu/hour input you will get about 1 gallon of condensate.

    if the boiler is in full condensing mode
  • HomerJSmith
    HomerJSmith Posts: 2,834
    I depends on the temperature of the combustion air drawn into the boiler, I think.