How not to fix a malfunctioning oil delay valve
Steamhead
Member Posts: 18,404
in Oil Heating
We upgraded the burner on this older American-Standard boiler at least a decade ago, and whoever maintained it thereafter did this:
I won't mention the oil company's name, but it's one of several Star Gas owns in the Baltimore area. We put a new valve on and upgraded the primary.
Consulting
Consulting
1
Look at what isn't connected to the valve.....................All Steamed Up, Inc.
Consulting0 -
I have done that just to get through the night if I didn't have a valve
at least they could have gone back and changed it0 -
That delay valve was a good idea for a clean startup and clean shut down of the burner. Makes maintenance easier when the nozzle assembly is not all gunked up with black carbon coating everything. I agree with @EBEBRATT-Ed. In a pinch, you need to do what you need to do. Then the customer decides to cancel the return trip with the replacement part (now that it is working) and the temporary fix becomes permanent. You never know what the circumstances were.
You did the right thing getting it up to today's standards with delay on and hopefully delay-off too.
Yours truly,
Mr.Ed
On that valve normally what goes wrong is the connection to the disk that gives the delay under the tape .We use to spin the two wires together ,which bypassed the disk and the valve works again, but with no delay .
This is what's on there now. We keep these on the truck, as should anyone servicing oil burners:
https://ordering.fwwebb.com/woitem/247220*1?CAWELAID&gclid=CjwKCAiAl4WABhAJEiwATUnEF27emKF5huemcBmO3fqEMAEKuCOvrrctVvn4aEDzZO-A3un7S48BbxoCq90QAvD_BwEAll Steamed Up, Inc.
Consulting0
