Crane 100 series boiler

kurtk
kurtk Member Posts: 4
edited January 2021 in Gas Heating
installing a new gas valve . need recommended gas pressure to burner. Crane 100 seris boiler

Comments

  • kurtk
    kurtk Member Posts: 4
    Have Kettling noise while firing. Descaled boiler , still have it. Suggestions of what else causes it.?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,517
    kettling is usually rust and scale and mud in the boiler. You can put boiler cleaner in and try boiling it out.

    Gas pressure is usually 3.5" of wc on the gas valve outlet going to the burners. Inlet pressure is a maximum of 12" wc, minimum should be about 5" wc.
  • kurtk
    kurtk Member Posts: 4
    thank you