Vintage radiant heating system mixing valve

bluemoon
Member Posts: 41


Hello Wallies....I'm hoping to get some input on a radiant control on a system that we are changing out from oil to gas. I'm sure this device is some sort of mixing valve & I'm not even sure if it is functioning, The 2" manifold supply X 12 3/4" loops is fed directly & teed to this device and also fed with the return water that is teed at the return. It also has 2 cables leaving the top of the valve off into the rafters (it's a ranch on slab)


that i'm guessing are sensors (abandoned?) . The radiant pump is controlled by a T-87 YoYo. There is a new homeowner & I have no maintenance history with this home & I have never seen this device. I would like to eliminate it if possible & install a conventional mix valve. Anyone familiar with this. I think it reads Sarcotherm (?). Please view the attached
0
Comments
-
That is definitely the mixing valve Hot Inlet is the “Hot” from the boiler supply . System Outlet is the “Mix” or reduced temperature to the floor loops. The last opening Pump Inlet is for a connection from the cooler “Cold” return from a tee on the radiant loop returns to the boiler.
Remove it and designed the replacement boiler as you would do with the proper mixing/injection design of your preferencesEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Agreed. My only hesitation is the direct supply in addition to the mixed0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements