Navien and CI radiators
Bill Julian
Member Posts: 164
in Gas Heating
How does the Navien 240 NCB take to CI radiators? I have a about 5 of them only on first floor.
I know I need the Mag filter. Thanks
A bit more information would be required. Any other radiation planned? Total heating load? Other small details?0
Need a good dirt/air separator to ensure the heat exchanger didn’t get fouled. The mag separator I’m not convinced is that big of a deal. We have several out there on cast iron without issues.A Combi works well with cast iron since it’s a high mass system.The one thing to watch is exhaust temp and flow rates. A combi must to be piped primary/ secondary and flow rates managed so return water temp is under 149 for PVC higher if you use a section of polypropylene. Ideally you use the lowest temp possible.A 240 only puts out around 120k for heating because of fixed max flow rate on the internal pump. At 120k that’s a 27f delta t. To get more capacity you need a higher delta T as you can’t increase flow any more. In domestic mode it will be over a 50f delta T at max output.0
Condensing boilers are designed to be used with low temperature radiation . Radiators fall under that list
What kind of cir what I need0
The other info is 5 radiators calculating to about 80,000 BTU
medium size couple smaller ones. First floor only nothing on 2nd.
My supplier says Taco 007 to move the water. He insists it will be fine!0
Are you wed to the Navien? I recently converted a old gravity system to a HTP UFT 80 modcon. Also piped it for DHW via a indirect tank.The UFT is a low head Fire tube boiler. I use a Grundfoss Alpha 2 on low constant velocity setting pumping directly through the boiler. GPM ranges from 4-5 when starting and 7-8 at temperature.How much square footage are you heating? I’ve got 11 rads currently active on three floors and even with very low water temps (105F) I’ll often get high (delta T 10-12F) return water temperatures.Keep in mind the BTU rating of the rads is a function of the water supply temperature and based on the 80k number you must have used 160 or 180F supply temperature in your calculations.I’d think your rads would have a hard time dumping that much heat to maintain return water below condensing temperature.I’ve included the link to my system drawing below.0
Cool thanks!0