2-zone hydronic baseboard system: zone 2 is always heating

tech0815
tech0815 Member Posts: 6
Hello, I just moved into a new home and the baseboard heating has two zones, one for the first and one for the second floor. Even when zone 1 is called, the radiators upstairs get more or less warm. The zones are separated by two zone pumps, but no zone valves. After running the system for some time on zone 1, both copper pipes after the two pumps are equally warm. When the system is started, the pipe for zone 1 directly after the pump becomes warm much faster than the one for zone 2. I think the zone 2 pump is not running when zone 1 is called for heat, at least I feel no vibration on the pipe.

My heating tech said that warm water moves up due to convection and suggested to add new zone control valves in addition to the existing zone pumps to block off this extra convection flow. Does this make sense? Is there a way to get a better zone separation with the existing zone pumps, without adding extra zone valves? I am wondering why the convection is so strong that the radiators in the second zone are quite warm. Thanks for any advice. In the photo, the pipe for zone 1 is on the left, for zone 2 on the right.


Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Don’t do that. It’s the most expensive remedy, if it’s even needed.
    First take a picture up a little higher. I want to see if there are flow checks installed.
    If there are you may need one serviced or replaced. If not, you can either install flow checks, switch out the circulates for IFC's.
    steve
  • tech0815
    tech0815 Member Posts: 6
    Thanks a lot. Here is the picture a bit higher up. Flow checks are actually a great idea, but I don't think that they are installed.