Options
PB1
Member Posts: 2
Hi, I have a Dunkirk boiler series PSB-5D. It’s about 20 yrs old. When our home thermostat calls for heat it heats up ok but will not shut off when the set temperature is reached. I have to switch it off manually. We have changed our home thermostat and the same thing happens so it must be a problem with the boiler. Any ideas?
0
Comments
-
How do you switch it off manually.....power switch or gas valve?0
-
It’s just a switch. Looks like a light switch.0
-
If power disconnect shuts it down and tstat is satisfied and off, then perhaps there is a sticking relay for the boiler.
You could disconnect the tstat wires at the boiler to see if it still stays on.
If you see the relay, there is also a high tech method to see if it is sticking....sometimes.
I take a rubber handle screwdriver and "thump" the body of the relay with the handle. If boiler shuts down that is it.
Pictures might help.0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements