Can anyone recommend the proper check for this recirc line?
Options
Timco
Member Posts: 3,040
It rattles loud enough to hear it across the house when it’s quiet. It’s been in for a couple months and has gotten worse. I’ve turned the pump down but now it’s doing it again. 



Just a guy running some pipes.
0
Comments
-
A soft seat, conical shape, low spring pop is what you want.
Low lead, of course.
NA51249 in 1/2 sweatBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
Thanks!! Will order today / tomorrow.Just a guy running some pipes.0