Are steam boilers cold starts?
itzasean
Member Posts: 71
So I was reading a bit on cold start boilers for forced hot water and it had me think does my steam boiler only start when the Thermostat on the wall tells it to or do they still cycle to keep the water at a certain temperature but not enough to produce steam ? I have a gas burnham independence boiler .
It would be a cold start.
The wall tstat controls the starting and stopping.
Now your pressure control may stop it if it reaches the pressure setting, as the pressure drops then the boiler fires again, this cycle will continue until the wall tstat is satisfied.
Short cycling because of the pressure control in not favorable, you could need more steam main venting, pipe insulation or the boiler is too large. (often the case) Or if it is a mild temp day.
However being cast iron, it may still be warm for the next tstat call for heat.
But if you heat your domestic water with the steam boiler, the boiler will fire up just for the water heating. It should not get hot enough to steam.1 -
Why would it start up again when the pressure drops if the temperature in the house is at or above the thermostat setting?0
The tstat is the first control in charge, the pressure control is next in line.....maybe some other safety switches...but most likely the pressure control will do the cycling while the tstat is calling for heat.
It would only restart on pressure drop if the tstat is not satisfied.
It may be cycling on the pressure switch and you are unaware of it.1 -
If it does have a coil for DHW or has a hot water heating loop, the controls for that could be set up as either cold start or warm start although warm start is far more common because it is simpler, it is just an aquasstat in parallel with the thermostat that keeps the boiler at the temp needed for the hot water system all the time.1