Protecting against cool return.

Options
icy78
icy78 Member Posts: 404
Basically, why?
Water heaters heat cold water in everyone's house, without any mixing. And without any issues.
I've seen numerous domestic HW boilers inputting 50f water, no problem! No one even blinks at that setup.
So what's the big deal about return water temp.?
I think it's only an issue if the burner low fires, and the flame/fluegas is cooled below condensing . At high fire, no problem.

Ok, I'm ready for a beatdown!🙂

Comments

  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    I'm not sure what you mean by "domestic HW boilers" but I think you mean water heaters which are throw-away items, though some are made of copper for condensing. You can't treat a boiler like a water heater. But you're right, cold return temperature is only an issue during an active burn. It's the excessively cool combustion gas temperatures that cause condensation.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • icy78
    icy78 Member Posts: 404
    Options
    JohnNY said:
    I'm not sure what you mean by "domestic HW boilers" but I think you mean water heaters which are throw-away items, though some are made of copper for condensing. You can't treat a boiler like a water heater. But you're right, cold return temperature is only an issue during an active burn. It's the excessively cool combustion gas temperatures that cause condensation.
    ...... well, the boilers I see are  often Raypak from 200- 750000 BTU. And they are  moving 20- 70 GPM through them and never any problem of boiler sooting or poor combustion, as long as it runs on high fire. (These are ribbon burners.)
    So 50^F in and 170 out.

    Small pool heaters too. Some have those governer devices to keep 105-110 LEAVING water temp but as long as they fire hard, theres no problem.
    I'm wondering if pushing inlet mixing is just a way for manufacturers of conventional atmospheric  boilers, to get those boilers used in situations where low fire is  an often seen firing rate. Because in that type of situation, inlet mixing might be a good thing.
  • mattmia2
    mattmia2 Member Posts: 9,639
    Options
    It probably has more to do with lower load periods of time and the thermostat getting satisfied before the supply temp gets much over 130 or 140 than the return temp directly.
  • Tinman
    Tinman Member Posts: 2,808
    Options
    Take a cast iron boiler and return 110* water to it and see how long it lasts. It’s not a marketing scheme. It’s based on true and tried science. 
    Steve Minnich
    icy78STEVEusaPA
  • hot_rod
    hot_rod Member Posts: 22,134
    Options
    I think it has to do with the design of the heat exchanger. The small Raypak boilers have always had a bypass valve to help return temperatures.
    All cold start boilers start out as condensing boilers, it matters how quickly they get above condensing temperatures, also that they run long enough to dry out the flue piping to prevent
    condensation.
    Some suggest tank type water heaters are built with "sloppy" somewhat inefficient heat exchange design so they can handle that mode of operation, Observe one running with cold water they drip and hiss until that flue passage warms sufficiently.
    Flue temperature tells the story as well as low efficiency numbers.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    STEVEusaPAicy78
  • mattmia2
    mattmia2 Member Posts: 9,639
    Options
    that looks like one of those brick barbecues..
  • icy78
    icy78 Member Posts: 404
    Options
    Take a cast iron boiler and return 110* water to it and see how long it lasts. It’s not a marketing scheme. It’s based on true and tried science. 
    Oops my bad!
    I bet your right Steve.

          I realized after you posted the above, that I  was thinking copper fin ,because those are what I've seen with low low inlet water temps.
          I think theres only 4 CI boiler that i can remember( that we service at least) and those had a high return temp. and are PS piped.

            So this conversation would be about copper fin boilers in low inlet temperature applications.
    Lots of Lochinvar, Raypak.

  • icy78
    icy78 Member Posts: 404
    Options
    hot_rod said:
    I think it has to do with the design of the heat exchanger. The small Raypak boilers have always had a bypass valve to help return temperatures. All cold start boilers start out as condensing boilers, it matters how quickly they get above condensing temperatures, also that they run long enough to dry out the flue piping to prevent condensation. Some suggest tank type water heaters are built with "sloppy" somewhat inefficient heat exchange design so they can handle that mode of operation, Observe one running with cold water they drip and hiss until that flue passage warms sufficiently. Flue temperature tells the story as well as low efficiency numbers.

    Interesting pic @hotrod.
    Yes I think that fluetemp is the main factor.
    It could be 45 degree f EWT and if the flue was above condensing then no problem. I think.