Wiring a thermostat without a C wire
Brianfrench
Member Posts: 4
I have a Taco SR506 relay connectedto a HTP Elite gas boiler. I have 3 zones of heating with hot water baseboard. I have 3 Lennox cooling air handlers in the attic. There are only 5 wires, RH and W go to the Taco relay. It is next to impossible to run an extra C wire through the walls and ceilings. I see there is a SA11 module, however with my system Taco ST506 for heating and Lennox CBX25UVH-024, 2 units and Lennox CBX27UH-030, 1 unit.
how do I wire the SA11? Is it possible to add a 1,000 ohm 1/2 watt resistor in the Taco SR506, and move the W wire to the C terminal in the, Emerson Sensi Touch Smart Thermostat SKU: R5000.45, thermostats?
You sure you need the G? Swapping g to c is common. We often jump y and g and the ahu if we need to grab a C
also, if your air handler and boiler are close (can run a wire between the two), you can use the rH and w for ahu wiring now. In this case you set up a small RIB relay to operate the boiler. Small pain but now you have two more wires
also, Honeywell has their 2 wire with interface module is none of the above suite your fancy2 -
I pulled out the wires and, yes - only 5 inside the jacket.HVACNUT said:Are you sure theres not another wire that was cut back to the jacket?
You can't use white as a Common. It's needed to complete the circuit through the thermostat. The resistor goes between C and W in the SR506.
The SA11 looks like it was tailor made for that thermostat.Inside the Taco relay, the R and W terminals connect to the red and white wires respectively.There is a 24 volt set of auxiliary terminals in the Taco relay.The instructions for the SA11, do not show the Taco application, only gas furnace.I did see the Fast-Stat FSCM00, which shows my type of application.I am wondering if the SA11 could be wired the same way?
Thank You Very Much ; Brian0 -
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Fast-Stat-FSCM00-Install-Instructions.pdfBrianfrench said:
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Fast-Stat-FSCM00-Install-Instructions.pdfThe Fast-Stat installation instructions0