Old McDonnell Miller Round Port Model 47-2 maintenance
Precaud
Precaud Member Posts: 378
My steam boiler has a M&M 47-2 LWCO with auto-feeder. I'm doing annual maintenance. The feeder is the older version with the round port. It works fine and has been a very reliable combo.
Removing and cleaning the strainer was obvious, and am now trying to remove the cartridge for cleaning. The manual instructs to use a 13/16" socket, but that apparently applies to the newer cartridges; the nut inside this unit is smaller than that and doesn't look like the manual's drawing. Before forcing the issue and removing it I thought it wise to check; is the cartridge on the older version removable for cleaning? Or should I just leave it alone?
1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • JUGHNE
    JUGHNE Member Posts: 11,492
    Round port indicates built before 1995.
    M&M recommends replacement every 10 years.
    You can replace the water feed cartridge assembly with new version. But by the time you spend with that and you should also crack the bowl open and look inside.
    Repair parts add up to a new one pretty quickly.
  • Precaud
    Thanks but the question is not about replacement. The unit works fine, I'm just doing seasonal maintenance.
  • JUGHNE
    Maintenance should include opening the bowl to clean it and the float inside.
  • Precaud
    Understood, but that is not what my question is about. It is SPECIFICALLY about if the cartridge on the older models are removable for cleaning.
    Anyone have experience with this?
  • retiredguy
    retiredguy Member Posts: 1,066
    I repaired many of these but I do not know what you are calling the cartridge. I used to carry parts in my truck many years ago to completely rebuild both the #47 and the $51. I never had to disassemble anything that required a 13/16 socket. So I am going to say no . You sometimes have to replace the cam for the #2 switch, the strainer, and on rare occasions the float. If you have to replace anything else, it may be better to replace the whole control.
    Precaud
  • Precaud
    Perfect, thank you, @retiredguy . I think it's good to go, then. The manual for the old version doesn't say anything about the cartridge, but it mentions cleaning the strainer only in passing in the troubleshooting section. The manual for the new version is more explicit about maintenance.
    EBEBRATT-Ed Member Posts: 18,715
    edited May 2020
    Nobody usually fools with cartridge they just replace the whole valve and strainer assembly.
    A homeowner has all the time in the world to fool with things and that's fine if you have the time I have no issue with that. M/M parts are $$$
    Most contractors can't take the time to rebuild a control unless it's a simple repair the labor cost will exceeds the value of the control especially with a 1995 control. You get a call back and your screwed
    And if a contractor rebuilds a 25 year old control which the MFG gives a 10 year life and if fails and cooks the boiler guess who looses.
    @Precaud not putting down what your doing, just explaining why many won't know about some of the internals
  • Precaud
    Thanks for the explanation, @EBEBRATT-Ed , it makes sense. If I were doing this for hire, I wouldn't screw around with it, either, for the reason(s) you said.
    That said, on the newer (post-1995) 47-2, this maintenance (along with cleaning the screen filter) is pretty easy to do.
    mattmia2 Member Posts: 14,414
    I suspect since the boiler is leaking a little you want to put as little in to the controls as safely possible.
  • Precaud
    That. And, if it ain't broke...
  • dopey27177
    dopey27177 Member Posts: 916
    Here is a cautionary note.
    I got involved with a dry fire on a brand new 350 horsepower boiler.
    The boiler was equipt with a McDonnell Miller 150 MD LWCF and pump controller and Model series 63 LWCF.
    Some time during the first heating season (1 month old) the boiler dry fired and 50 tubes melted.
    When an inspection was done by Hartford boiler and McDonnell and Miller it was found that some one had taken the the 150 MD apart and did some kind of service on the control. Additionally the series 63 control was not wired correctly, it did not shut down the boiler.
    Fortunately there was a log book in the boiler room where a service tech from the boiler installer company came on a no heat call. He found a problem with the auto feeder. He found the float ball was stuck in the up position which prevented the pump from filling the boiler with water.
    What was strange was the inspectors claimed the 63 cutoff was wired incorrectly. I say this because when the tech came on the no heat call the shut down on low water, there fore there was no wiring problem with the control.
    Fortunately my customer had me come to the building to meet with the inspectors.
    I had a discussion with them about the wiring of the 63 LWCF.
    Since I am no control person or electrician I asked them this question. When there was a heat complaint how come the was out on low water. Additionally the tech tested the 150MD and the 63 LWCF for operation and he noted in the log book the pump control and lwcf combo and the 63 LWCF worked as intended.
    Here are two lessons.
    1. Have your customer keep a log book in the boiler room and have your techs make the service entries.
    2. Question insurance inspectors on their findings, people make mistakes.
    I only put this comment in this discussion because when you fix a LWCF you take the responsibility of he boiler on your head.
    Hopefully you have liability insurance and an error of omission and commission policy to cover you if you screw up on a repair of a safety for a boiler.
    Jake
  • retiredguy
    edited May 2020
    This is my experience with a low water control being miss wired similar to what @dopey27177 wrote about. The company I worked for discovered a situation with a MM #157 LWCO as the primary control and a back up secondary MM #63 on an H B Smith Boiler where the limit feed for the #63 LWCO boiler control and the control "out" wires were switched. Both controls utilized the alarm terminal to announce that a low water condition existed. Either control would shut down the boiler when operated by itself when "testing" (blowing down) but when both controls operated under normal operating parameters, the primary control would shut the boiler down safely. Then, if the water level continued to fall due to the boiler still producing steam, the secondary control, the MM #63, would also open the limit circuit. Due to the miss wire the result was that the alarm circuit on the second control would then put power back into the limit circuit and allow the boiler to fire normally. The result of course was a dry fire and boiler melt down. This happened when both controls were wired utilizing the alarm terminal. The fix was to never wire the secondary LWCO utilizing the alarm terminals. . The melt down was caused by a service tech switching those 2 wires in the course of normal LWCO maintenance. Switching the limit circuit in and out wires caused a major catastrophe. However removing the alarm terminal wire corrected this potential problem. My employer was charged with this mistake and resulted in an insurance claim.
  • Champ6
    Champ6 Member Posts: 20
    My boiler is having feedwater problems with this McDonnell #47. I can manually lift the valve and get water in, but it does not work on it's own. Is it likely to be the valve or the float? as a homeowner and not a pro, I'd like to fix it right the first time and not just throw parts at it.
    @Champ6
    If the float is staying down it could be"
    A hole in the float weighing the float down
    A valve in the 47=2 feeder discharge pipe could be closed
    The control itself 47-2 is plugged with gunk or the 1/2" pipes that connect it to the boiler could be plugged up
    Proceed with caution...that control may be the only one protecting the boiler from low water.
    Check "find a contractor on this site" or post where you are located
  • JUGHNE
    edited October 2021
    How old is this control?
    Does the port where the water pipes connect have a hex shape or is it round?
    If the float will not drop down to feed water than it may not shut the burner off on low water.
    This is of serious concern. That is supposed to add water and if it does not the float drops a little more it should switch off the burner.....and keep it off!.....danger of dry fire and even explosion if it or you unknowing decide to add water to a red hot boiler. That water flashes to steam by a factor of 1700.
    This is what makes the evening news.
  • Champ6
    This is a round port LWC, but it is set up only to add feed water. The W-M boiler is dated 1994, so I'd guess this is the same age, but who knows. There is a separate, and more modern looking LWC that possible also controls the damper, so regardless, the boiler shuts off if the water drops too low. Why it was set up this way? who knows, but I don't like blowing down the boiler and having to fiddle around with this. If it looks too crusty, I may just plumb in a ball valve to top it up.
  • Champ6
    Problem solved. I started to remove the cartridge, and despite having PVC from the street, a whole house filter, and copper near the boiler, that screen was NASTY! Where did all of that rust, and HUGE flakes too, come from? I cleaned it up, put it back, and it works fine. Next step tomorrow will be to remove the bowl of the unit and check for rusk clumps and stuff. I clear this often, but after this screen incident, ant to make sure the float isn't being compromised.
  • JUGHNE
    So are there any wires connected to this #47?
  • Champ6
    There were, but they've been cut. Now there is another LWC wired in. Even though we have no or minimal leaks, this is the only way to refill the boiler, and it is kind of nice that it tops it up should it be necessary, but I blow it down a couple of times a month.
    Now, is "blowing down" the correct term? Boiler is cold or maybe warm, but not hot or firing. I drain the M&M and it refills.