one zone will not start boiler
Jethro789
Jethro789 Member, Email Confirmation Posts: 1
I have a hot water baseboard boiler made by The H.B. Smith company and one of the zones will not start boiler, the zone does open and the boiler makes a click noise but will not fire up. What can cause this issue?
  • kcopp
    kcopp Member Posts: 4,667
    But other zones will? Sounds line a wiring issue. Broken wire on that end switch? Any chance at a pix?
    BillyO
  • BillyO
    BillyO Member Posts: 277
    bad end switch on zone valve
    mattmia2SuperTech
  • unclejohn
    unclejohn Member Posts: 1,833
    Boiler makes a click, maybe bad relay at boiler.
    mattmia2 Member Posts: 16,574
    edited March 2020
    the click from the boiler would suggest that we need some pictures to figure out how it is set up. Could be it is firing the boiler when the zone calls but the end switch isn't starting the pump if it is wired that way. The boiler might not be firing when you observe it because it has shut off on high limit because it is not circulating.
    BillyO