TPI Aquastat Wiring
sasquatch16
sasquatch16 Member Posts: 10
Looking for some guidance wiring aquastat on new indirect water heater. Current aquastat just uses 2 low voltage wires. I believe they are 24v hot and aquastat makes and breaks connection. New TPI aquastat has 2 wires in and 2 out. Does this have to have
a common wired to it to work?
  • sasquatch16
  • STEVEusaPA
    We're missing a whole lot of information before making some suggestions.
    Typically the indirect is it's own zone, either controlled by circulators, or zone valves.
    You'll need to supply 24 volts from a transformer or from a zone control.
    Some zone controls and boiler controls have terminals for an indirect so to control it's own zone.
    What type of new indirect and why wasn't it supplied with an aquastat that isn't 50 years old?
  • sasquatch16
    New tank supplied with the new aquastat pictured. Current setup has its own circulator on boiler with 2 wires hooked up to old aquastat that go to control
  • kcopp
    kcopp Member Posts: 4,610
    The 2 terminals on the left go to the TT like there was on the old aquastat... You need to run 24v to the other terminals on the right....
    http://www.vaughncorp.com/downloads/tpp/TPI Wiring.pdf
  • sasquatch16
    Thank you