Burnham Furnace - Steam heat

cj_bruno
cj_bruno Member Posts: 1
I noticed that i had a significant amount of exhaust coming out of my chimney flue compared to my neighbors and I'm wondering if this is normal in the winter months, or if could be something else.

Other thing I noticed is that the water is automatically filling a bit more often. It levels out a few times a day.

Comments

  • Fred
    Fred Member Posts: 8,542
    edited January 2020
    Most likely indicates that at least one of the cast iron section has rusted through, above the water line, sending steam up the chimney. Time to take the jacket off of the boiler or at least the top cover and see what's there.

    You can also shut the boiler down, let it cool a little and over-fill it and see if water runs out onto the floor.
  • JohnNY
    JohnNY Member Posts: 3,226
    Shut off the boiler.
    Fill the boiler up to the top of the glass gauge and then add some more water until it is probably filled to the top.
    Open the relief the valve to check to see if the water is there yet.
    If water leaks out from under the jacket, you’ve got a leaking boiler.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • JUGHNE
    JUGHNE Member Posts: 11,042
    Where are you located?
    Check above on the main site for "Find a contractor".
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,951
    edited January 2020
    In all likelihood , there is a leak in the upper part of the boiler. Steam will leak out the top and go up the chimney
  • B_Sloane
    B_Sloane Member Posts: 56
    Copper does have many times the expansion of Steel pipe
    but it is unlikely that in the very short length of the Header there was significant stress on the Sections
    There is a substantial amount of clamping force exerted by the tie bolts
    I would expect the copper joint to fail long before a section moved enough to leak
    someone advised letting the boiler cool, and over filling it
    that was good advice
    you should remove all of the Jacket that is practical, some will be trapped by piping, or controls