Pressure relief valves?
JackW
Member Posts: 236
The picture below shows two pressure relief valves on the same line, why would you need that?
Thanks,
Thanks,
You don't. Keep in mind this set up is not perfect, what you do need on those reliefs is a drop pipe to within 6" of the floor. Looks like this designer was more interested in filling up his board with ups and downs of piping. Safety drop piping must not have met his standards for the look he was going for. The gas piping is questionable also, but hard to tell how it is actually done. Glad he found a place for that wrench
D1 -
That's gotta be a classroom or something. No cold water fill.0
DZoro I plan on following this plan, if not per say, then pretty close. What would you change?0
HCVAVNUT what is the valve to the left of the 90 degree elbow going into the return side?
HomerJSmith what would you change?0
JUGHNE then the first relief valve is where it should be, and no need for the second one.0
Could be Dale, maybe one a backup just in case.0
It is a nice looking installation, but I would have done it differently.
There are too many 90 deg fittings. I would have carried the primary loop straight across and put the pumps to the zones under the primary loop and eliminated the U piping on the outlet to the pumps. I don't see a need for that many gauges. I don't know whether you have concentric venting, which I never do, but I usually put a PVC tee on the air intake with a drain loop of 1/2" vinyl tubing to catch any water that might enter the air intake and drain it out before it can enter the boiler.
I don't see a need for two pressure relief valves, either. A pressure relief valve should be within 6" of the boiler.
Zman's suggestion of off-setting the expansion tank will keep any debris from getting into the tank that's pulled out of the air eliminator. Putting isolation valve and a drain valve makes it easier to charge the tank when that needs to be done.1 -
Thank you Homer for the ideas, any chance you could draw me a diagram? I understand what you are saying, not sure where to go with it.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 71 Pipe Deterioration
- 999 Plumbing
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
