Navien NR 240A

Options
Tony1953
Tony1953 Member Posts: 5
constant water trickling out the condensate line when unit is off
could it be the heat exchanger? or 3 way valve?

Comments

  • DZoro
    DZoro Member Posts: 1,048
    Options
    More than likely the heat exchanger. What boiler do you have?
    D
    kcopp
  • DZoro
    DZoro Member Posts: 1,048
    Options
    My bad,, you have a Navien, how old? Have you had any water testing done?
    D
  • Tony1953
    Tony1953 Member Posts: 5
    Options
    it is a NR240A
  • Tony1953
    Tony1953 Member Posts: 5
    Options
    no error codes and it works normally
  • Tony1953
    Tony1953 Member Posts: 5
    Options
    9 years old
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    @Tony1953 yeah that sounds like a leaking heat exchanger
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    kcoppMikeL_2delta T
  • Tony1953
    Tony1953 Member Posts: 5
    Options
    what about the water inlet valve is not closing completely?
  • Alan (California Radiant) Forbes
    Options
    If your fill valve overfills the system, the pressure goes up. If the pressure goes over 30psi, your relief valve will open and leak water, not your condensate line.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab